Yep but what 5 second requirement I can't see one except 5 sec is for distribution circuits of & above 32amp ?
Those are your cases for a 5s disconnect time, subject to thermal limits on the cable (e.g. adiabatic check).

Normally you would always aim for 0.4s or below even if not explicitly required, but there are cases when you look at the 5s limit. For example:
  • For high current sub-main or fixed circuits you may not be able to meet 0.4s due to Ze anyway
  • On a sub-main you might push the upstream OCPD as high as the 5s or adiabatic thermal limits allow to get better selectivity with the down-stream DB MCBs.
[automerge]1590238260[/automerge]
yeah both aren't really needed if you just do the simple equation.
Except when the simple equations is very wrong. Yes, if you know it is a B-curve MCB, but in other cases you can get it wrong by a factor of 2 or so.
 
Those are your cases for a 5s disconnect time, subject to thermal limits on the cable (e.g. adiabatic check).
The OSG book in Appendix B has tables that include the typical adiabatic limit for the common CPC sizes so it is your easiest option for selecting an OCPD when desiging something like a garage CU feed, or verifying an existing OCPD and measured Zs is reasonable.
 
has anyone seen this video ? 35 is the Magic Number

To view this content we will need your consent to set third party cookies.
For more detailed information, see our cookies page.
View: https://m.youtube.com/watch?v=URBD4llLU6Y


at first I was thinking, what! this makes no sense see post 10 but it does make sense and 35 is the magic number - bit of fun figuring out why if anyone wants to have a crack.
 

Reply to Max zs values in the Electrical Engineering Chat area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock