tom262

Help!!! I've been asked to work out the maximum demand for a new property for the DNO, I believe I have worked it out correctly applying diversity (something I've hardly looked at since college) but it seems abit high.

there will be 12 potential circuits.
1. 32amp cooker
2. 32 amp hob
3. 32 amp ring
4. 32 amp ring
5. 16 amp radial (sockets)
6. 6 amp lighting circuit (20 10w led downlight and 5 5amp sockets)
7. 6 amp lighting circuit (20 10w led downlight and 2 58w twin floersent)
8. 6 amp lights circuit (5 10w led downlight, 3 extractor fans, 10 outside lights 40w each)
9. 3kw immersion heater
10. 20-32 amp air source heat pump (unsure on size yet)
11.solar pv
12. 40 amp shower circuit (may not be used)

After applying what I believe to be the correct diversity I have a total maximum demand over 100amp this seems abit high??
thabks in advance Tom
 
Help!!! I've been asked to work out the maximum demand for a new property for the DNO, I believe I have worked it out correctly applying diversity (something I've hardly looked at since college) but it seems abit high.

there will be 12 potential circuits.
1. 32amp cooker
2. 32 amp hob
3. 32 amp ring
4. 32 amp ring
5. 16 amp radial (sockets)
6. 6 amp lighting circuit (20 10w led downlight and 5 5amp sockets)
7. 6 amp lighting circuit (20 10w led downlight and 2 58w twin floersent)
8. 6 amp lights circuit (5 10w led downlight, 3 extractor fans, 10 outside lights 40w each)
9. 3kw immersion heater
10. 20-32 amp air source heat pump (unsure on size yet)
11.solar pv
12. 40 amp shower circuit (may not be used)

After applying what I believe to be the correct diversity I have a total maximum demand over 100amp this seems abit high??
thabks in advance Tom

How is the property being heated? If Gas, possibly no need for Imm /Htr and or elec shower.
OPPS >>>> ASHP
 
How is the property being heated? If Gas, possibly no need for Imm /Htr and or elec shower.
OPPS >>>> ASHP
Air source hear pump,
'the cooker and hob I've done, 10A +30% for each
the rings as 32 plus 16 for the total of the two
the immersion plus the radial 16A for each
the lighting as 66% of each added together





unsure re on the PV and heat pump.
 
better way..... you want DNO to fit a 100A fuse, so you tell them your MD is 90A. ssimplesss.
 

Reply to Maximum demand in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock