Currently reading:
N/E fault RCD not tripping ??

Discuss N/E fault RCD not tripping ?? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
34
Hi all

can anyone give me the logic why the RCD wouldn’t trip on a neutral/earth fault. Testing a extension where they have added in 5 additional sockets to the upstairs ring had been powered up and nothing tripping with household appliances plugged in and working. Carrying out IR tests to find had dead short on one leg of the neutral and earth between 2 sockets but there was no issue of tripping ? RCD checks out ok with test button and RCD tests. Have disconnected this leg and then fitted fuse spur off the ring to carry the additional sockets now as to late to add in additional cable, so extension spurred off ring using fuse spur. Would it be the case that it had seized a bit RCD or that its connected to a TNCS system?? Replies much appreciated ?
 
it has been known for a N-E fault to inhibit the RCD from tripping, even on the test button. don't know the theory behind it, but i have seen it a couple of times.
 
Aww ok thanks for the reply ?. Had also a couple of other issues never seen before.

Trying to carry out Zs test on upstairs lights and found that it would carry out test as error code of >65 fre. Looked at the manuals and states supply frequency to high for test. So I disconnected the dimmer switch and managed to carry out test. Seems the dimmer is causing the frequency issue but don’t know why this would be as should be rated for 50hz ?

another issue think I know the issue on this one though IR test on socket circuit live to earth dead short. Join live and neutral together test down to earth >999mega ohms. Thinking with me going live to earth IR test travelling though USB ports on the sockets ? I noticed behind a cabinet was causing reading to be dead short. This is the only reason I can think of as unable to switch off USB ports ?
 
If you know there are usb sockets in the circuit, testing N-E insulation is a bad idea.
you can't say there is a dead short if testing with an insulation resistance tester.

I would only consider something to be a dead short if measured below 1 ohm.
 
Hi yeah I tested live to earth but coming up 0.00mega ohm but link neutral and live together then test then all clear >999 mega ohm so it’s like I’m testing through the USB when doing live to earth on the IR tests ?
 
Hi yeah I tested live to earth but coming up 0.00mega ohm but link neutral and live together then test then all clear >999 mega ohm so it’s like I’m testing through the USB when doing live to earth on the IR tests ?
If your neutral is disconnected from the neutral bar you should not get zero as your linked neutral/line to earth was clear.
 
Sorry I may not have followed things here fully, but if you are reading zero N - E but everything works etc then I’m thinking perhaps you’re recording the excellent N - E connection at the cutout?
 
But regarding the USB sockets. If I have not disconnected the neutrals from neutral bar and tested between live and earth and I am getting low reading basically zero near enough, this should be because the USB points are bringing the reading down as I will be going through the earth and being TNCS will be linked to neutral so will be testing the USB point. As when I link out live and neutrals at the consumer unit and go to a socket then test live to earth insulation resistance it comes out clear. >999mega ohms. Now if that was a damaged cable that would be picked up, does that make sense ?
 
But regarding the USB sockets. If I have not disconnected the neutrals from neutral bar and tested between live and earth and I am getting low reading basically zero near enough, this should be because the USB points are bringing the reading down as I will be going through the earth and being TNCS will be linked to neutral so will be testing the USB point. As when I link out live and neutrals at the consumer unit and go to a socket then test live to earth insulation resistance it comes out clear. >999mega ohms. Now if that was a damaged cable that would be picked up, does that make sense ?
What voltage are you doing insulation resistance test?
 
On both tests at 250v and 500v. I tested live to earth at 250volt seen that it was very low near enough zero, now this has been connected to a RCD and MCB for years this circuit. So I then joined live and neutrals together at consumer unit then tested live to earth IR test at nearest socket comes up >999mega ohms. So I am thinking I’m testing through the USB points when carrying out live to earth only with neutrals still connected to N bar ?? That make sense
 
On both tests at 250v and 500v. I tested live to earth at 250volt seen that it was very low near enough zero, now this has been connected to a RCD and MCB for years this circuit. So I then joined live and neutrals together at consumer unit then tested live to earth IR test at nearest socket comes up >999mega ohms. So I am thinking I’m testing through the USB points when carrying out live to earth only with neutrals still connected to N bar ?? That make sense
Testing at 250v is only beneficial when there is a fault so that you don’t need to subject circuit to 500v however you need to carry out insulation resistance test at 500v to record accurate fault reading and true scale of insulation. I’m trying to test you here ?
 
Testing at 250v is only beneficial when there is a fault so that you don’t need to subject circuit to 500v however you need to carry out insulation resistance test at 500v to record accurate fault reading and true scale of insulation. I’m trying to test you here ?
I’m here to learn just like yourself and Aslong as it’s done appropriately then there is no harm. Best way is to ensure everything is unplugged from sockets
 
No it’s 6 months old, that’s why I am thinking I’m testing through the USB ports only thing I can think of as if it was a dead short then it would show up on L- N together and test to earth as well but it’s clear ?
 
No it’s 6 months old, that’s why I am thinking I’m testing through the USB ports only thing I can think of as if it was a dead short then it would show up on L- N together and test to earth as well but it’s clear ?
Well disconnect the usb sockets put the cables in connector blocks then test. Make sure you are disconnecting the circuit in question out of bar/mcb to ensure it’s definitive. I’m a bit confused here sorry it’s late and been working 14 hours again ?‍♂️ You’ve been called back after 6 months and it’s tripping?
 
Well disconnect the usb sockets put the cables in connector blocks then test. Make sure you are disconnecting the circuit in question out of bar/mcb to ensure it’s definitive. I’m a bit confused here sorry it’s late and been working 14 hours again ?‍♂️ You’ve been called back after 6 months and it’s tripping?
The USB ports will 100% interfere with you’re readings and give false readings disconnect them. So the fault is on the sockets? Unplug everything and then carry out insulation resistance. Once established that the fault is on the ring main. Most likely pain in the arse is N-E fault split the legs at consumer go to half way point of ring (take an educated guess) then you will know which side the fault is on)
 

Reply to N/E fault RCD not tripping ?? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top