That's a picture of the supply fuse coming into the house i'm working on, all I need to do is change the Db, easy enough, all happy with that. Only question is how do I isolate the Db and make it safe to work on? the fuse in tagged in so can't be removed without cutting the tags but I'm not sure what issues might arise with the suppliers if I cut them. Theres no switch on the fuse unit to simply isolate. Need advice asap.
Cheers
 
well for a start....i am not encouraging potentially dangerous practices...such as pulling bullits....or going into the meter terminations...and disconnecting there.....
what i will say is this...you either:
1)wait for an age for the DNO/energy supplier to come out to interrupt the supply for you
2)as above....and have a DP iso fitted at the same time
3)disconnect yourself...a cheaper and quicker alternative
If an energy supplier sees that the meter seals have been cut...then it swings 2 ways:
Has any recent work been carried out that required a power outage to that property?...such as a board change..or:
Has no recent work been done there.....power theft?
the DNO will also take the same view...well should do anyway...
 
Seeing as these meters can be remotely programmed, credit added etc., I wonder if they can be remotely switched off?
Worth checking if you're getting in contact with the supplier.

edit...

Not really safe isolation though, it could be powered back up while your still working! :-(
 
Last edited by a moderator:
those henley blocks are on the customers side of the meter, so the outgoing tails could be taken out ( carefully, with the CU main switch OFF )
 
I've never had any problems with cutting the link and pulling the main fuse. My name is all over the new boards I fit and phone number with date I fitted board etc so wouldn't be hard for them to find me. But after 20 years fitting boards no calls from electric company's. if they fitted the isolators there would never be the need to pull the fuse.
 
I can't see the image as I'm on my phone but sometimes there is enough slack to wedge a screwdriver between the carrier and base and hold it apart with the seal intact. Other wise I've had to cut the tag, you can buy seals and tags online and re crimp them afterwards, but they won't have the markings on then from the DNO.
 
remove the red cable from the henley, job done

NO
Turn off the main switch on the consumer unit first = no load
Then remove both the red and the black cables from the Henleys. Remember Neutral is also a live conductor.

Looking at the Henleys, you still have to cut the DNO seals on there (why do they do that?)

To LEX

If you involve the DNO then they may require a BS7671 cert or other certificate of safety/compliance before reconnecting.

I'm hoping that you have a full set of calibrated test equipment so you can check your new consumer unit?
I am also hoping that you have (or will) notify the local authority before starting work, or are you a registered electrician?.
 
To LEX

If you involve the DNO then they may require a BS7671 cert or other certificate of safety/compliance before reconnecting.

I'm hoping that you have a full set of calibrated test equipment so you can check your new consumer unit?
I am also hoping that you have (or will) notify the local authority before starting work, or are you a registered electrician?.

I have a fluke for testing. I'm registered with JIB but haven't told the local authority anything just yet. I've spoken to the DNO, they are coming out to fit a proper isolator so this issue won't come up again.
 
Do these new meters not have the built in isolator, I can see a small black hole top right but can't tell what it is, if there's a slotted screw in there a ninety degree turn isolates it.
Personally I would just take the cables out of the henleys.
 
Do these new meters not have the built in isolator, I can see a small black hole top right but can't tell what it is, if there's a slotted screw in there a ninety degree turn isolates it.
Personally I would just take the cables out of the henleys.
well....from what i remember there was a hoo ha over this....the DNO didn`t like the idea of built-in iso`s as they stood to lose money.....shameful really.....elf n sayfti anyone?...
 
I have a fluke for testing. I'm registered with JIB but haven't told the local authority anything just yet. I've spoken to the DNO, they are coming out to fit a proper isolator so this issue won't come up again.

Hmm, what sort of Fluke meter will that be then.
Does it have Insulation Resistance, low ohm and RCD testing facilities?

also

Does JIB allow you to self certify and notify installations in accordance with Part P? I wasn't aware of that little loophole....
 
Hmm, what sort of Fluke meter will that be then.
Does it have Insulation Resistance, low ohm and RCD testing facilities?

also

Does JIB allow you to self certify and notify installations in accordance with Part P? I wasn't aware of that little loophole....

Yes its all singing all dancing, didn't realise I'd signed up for the Spanish inquisition.
Doing a favour for a mate not commissioning big Ben!
 

Reply to Need help with supply fuse in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top