Guitarist - Have you had any issues with your no trip readings as per the "known" problems with the 1700 series?

Basically, the 1700 series does not give accurate readings on the 2-wire no-trip setting, although on 3-wire I have found it to be fairly accurate. Lots of people make the mistake of carrying out a Ze reading on 2-wire no-trip and then can't understand why the Ze is so high. I have spoken to Megger about making this more obvious in the literature and they have said it will be looked into.

To summarise-

Ze readings - 2-wire high current setting - Very accurate

Zs readings (where no RCD is present) - 2 or 3-wire high current setting - Very accurate

Zs readings (with RCD in circuit) - 3-wire no-trip setting - Fairly accurate


Personally, I never use the 2-wire no-trip setting now, as without the reference neutral the reading is not accurate at all. Megger have told me that with an RCD in circuit, an inaccurate reading isn't a problem as we have a few hundred ohms to play with.

The above comments are purely my opinion after my own experience, testing and talking to Megger.
 
Personally, I never use the 2-wire no-trip setting now, as without the reference neutral the reading is not accurate at all. Megger have told me that with an RCD in circuit, an inaccurate reading isn't a problem as we have a few hundred ohms to play with.

The above comments are purely my opinion after my own experience, testing and talking to Megger.


This is pretty poor, I would have expected better from a premium brand such as Megger!, I have older Megger Equipment (in two instruments) the LRCD 220 and MIT320, and there are mistakes in the user manuals and in the updated online ones too!
Although the instruments themselves are OK, but again the (3-wire) no trip readings always give slightly higher readings than the high current readings, I now just record on the sheets the calculated Zs where possible, Ze+(R1+R2), and still carry out the no-trip reading just to double check.
 
My elecsa assessor advised calculating Zs by Ze +(R1+R2) on installation work, and measuring it with the MFT when testing and inspecting. High readings can then warrant further investigation. Seems like sound advice to me.
Spark 68, I was also very disappointed, but understood the limitations of the MFT once I'd had it explained. What I find almost unforgivable is that there was nothing in any documentation about this, and neither did tech support at megger help me on the phone. It was my 3rd e-mail which clarified it all. What a waste of my time and energy!
Actually, there is a line somewhere about 2-wire no-trip resting not always being accurate...
 
Well, an update. I had my 1720 calibrated this afternoon. All very accurate except the low current setting no trip facility. With three wire it was about 0.15 ohms too low and with a two lead test it was up to 0.3 ohms too low!

I have spoken to Megger and they will look at it. I have firmware version 1.06 so its rather behind the new firmware now out. I will report back once they have looked at it and my calibrator is going to re check it for me. That will be interesting. Megger state that "0.2 or 0.3 isn't bad"

Guitarist - This backs up exactly what you said above.
 

Reply to Newbie help with Zs test result please in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
Hi, can someone give me some advice RE completing a small works certificate for a fused spur coming from a ring final. 1) In part 2 of the AMD2...
Replies
35
Views
7K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Morning all So the site I'm based at recently had some work done (think partitioners). This package of work included electrical. This was...
Replies
47
Views
8K
Hi all, just a quick one to ask about an issue I'm having with my EV charger. I'll give a little background first but ultimately I want to know if...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock