- Reaction score
- 739
It would be more appropriate to say it eats up the current. The source of the voltage is the mains in series with a high impedance (often the inter-core capacitance of a length of cable) which approximates to a current source. Like earth leakage, if you pull it right down to earth / neutral potential via a lower impedance, whether that is a snubber, an actual lighting load or even a direct connection to earth, a certain current will still flow, equal to V/Xc of the cable capacitance.
We always talk of the earth leakage current because the voltage (from the CPC to the MET) is negligible and the sources approximate to current sources. But in these 'ghost voltage' situations people often say ''I'm reading V volts on my meter' because they were testing for voltage at the time, but it would be better to divide that V by the input resistance of the meter and say 'I'm reading I microamps on my meter'.
Seriously, where do you gain this level of knowledge?