....To fit old Sentry board.
Present board has 80A, 30mA RCD mainswitch, and it’s a 16 way board!!
I can’t get all circuits to stay on all at once. Have to leave any one of 3 lighting circuits off for rcd to hold.
Individually they work fine.
Accumulative earth leak between all circuits, dropping out the rcd which when ramp tested tripped at 19mA.
Have recommended changing all breakers to rcbo, and normal mainswitch. Either find RCBOs to replace, or all new board.
The old mcbs model numbers are. LN 5906, or 5916 etc.
Do new mk rcbo’s fit this old board?
Homebase are still selling their MK stock off cheap