Search the forum,

Discuss Over Voltage as SolarEdge SE3500 Error Code 33 Trips out frequently. 253v / 264v ? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

S

sja

Esteemed forum Members,

I had a 4kW Solar PV system installed in Dec ‘13 and since Feb and on an increasing basis with improving sunshine, I’ve seen my SolarEdge SE3500 invertor trip out showing Error Code 33, AC Over Voltage. I don’t know how accurate the device is but I can see on the Inverter faceplate LCD and on the SE Monitoring Portal that my local grid voltage is quite high (nearly always above 245v often in range 250-253v – sometimes spiking over). I can’t see many other solar installation near me but there is a DNO transformer down the other end of my street.

I see these trips multiple times a day – it looks like it might be occurring at 251v, 252v or 253v – and sometime my inverter is held hard-down for periods of up to 45 mins. I’m a bit worried that it is going to damage something in my new installation and of course it is impacting my production (and investment!) I can see there are similar posts on this forum but in trying to figure out how I will get to a resolution I’m trying to get a deeper understanding of the following points :

I will approach my DNO next week, UK Power Networks – is it likely that they can ‘fix’ my local supply so it is more in line with the UK harmonised standard of 230v? (Is it technically feasible that they could ‘fix’ issue possibly by ‘tapping’ the local sub-station transformer or doing something else?) If they are agreeable, how long might this fix take to implement?

Alternatively I see some references to G.83 or G.83/1 / G.83/2; what are these exactly? I’ve seen that BS 7671 Appendix 2 section 14. : The UK supply 230 V +10% - 6% ; translates as 216.2v to 253v. But I’ve also seen people refer to an upper voltage limit of 264v, often in relation to G.83/? Is it reasonable for me to ask UK Power Networks to allow me to have my installer re-configure my Inverter to trip at 264v? Either on a temporary basis while the DNO rectify the supply – or permanently if for any reason they are un-willing to do so? Do our UK standards allow them to grant that permission and any views on the likely outcome of my ask?

My installer has suggested that fitting a ‘Voltage Optimiser’ on my supply would give a good and probably the quickest resolution. While I remain open minded about this as a solution, at the moment I’m not convinced it is the correct resolution. Any views? I can see it will present my Inverter with a lower AC voltage, but what happens in the other direction when I am exporting? Will I be driving grid voltage >253v? Will the device actually allow export? Are these devices efficient and safe?

Thanks in advance.
 
Re: Over Voltage as SolarEdge SE3500 Error Code 33 Trips out frequently. 253v / 264v

Voltage optimiser will not help as it would be fitted house side of the inverter and therefor would not effect it.
 
Re: Over Voltage as SolarEdge SE3500 Error Code 33 Trips out frequently. 253v / 264v

what is the length of the cable run, and what size cable is it?

You want a minimum of 6mm2 on a 4kWp system, particularly so if the inverter is in the loft, some companies are installing using 2.5mm2 cable due to being run by idiots, and that will exacerbate any over voltage issues as the losses in the cable will push the voltage up at the inveter, more so the more the inverter is outputting. Your description would make me think this is the likely problem, as you're saying it's getting worse with more sunshine, which seems to indicate the problem is at your end not the grid (unless there are a lot of other solar systems connected to the same transformer).
 
Re: Over Voltage as SolarEdge SE3500 Error Code 33 Trips out frequently. 253v / 264v

If your installer suggested that a VO unit might help then I'd also question the AC cable size used - do you know, and what the length of the run is?
now it looks like I was just copying your post....
 
Re: Over Voltage as SolarEdge SE3500 Error Code 33 Trips out frequently. 253v / 264v

If the installation isn't satisfactory I think it should be your installer who should be chasing the dno no? Providing the volt drop of the circuit is within the manufacturers recommendations there shouldn't be much of an issue with getting an alteration to the supply voltage. If your installers are friendly with the local network it should be altered pretty swiftly.
 
Over Voltage as SolarEdge SE3500 Error Code 33 Trips out frequently. 253v / 264v

I forgot to mention in my original post that my inverter is in the garage right next to the consumer unit. There is a short run of AC cable into the unit; I'm not sure if it's 6mm2 but it's less than 1m in length. I doubt there's much voltage drop over it but it might be worth checking. (I am assuming the cable that Gavin A refers to is the AC cable and not the DC? My DC from loft to garage is anyway 6mm2)

Regarding Gary K's post about the Voltage Optimiser not working - can anyone explain the technical reason why and also the difference in the device's situation on the 'house side' (of the consumer unit? the electricity meter?) and other places it could be situated?

Thanks for your replies so far.
 
Re: Over Voltage as SolarEdge SE3500 Error Code 33 Trips out frequently. 253v / 264v

Can you post a picture of the inverter & consumer unit in the garage?
 
Re: Over Voltage as SolarEdge SE3500 Error Code 33 Trips out frequently. 253v / 264v

Regarding Gary K's post about the Voltage Optimiser not working - can anyone explain the technical reason why and also the difference in the device's situation on the 'house side' (of the consumer unit? the electricity meter?) and other places it could be situated?


If you read any VO installation manual (see a couple of examples below) you will see that the manufacturers' instructions are for any on-site generation, such as PV, to only be connected on the grid side of the VO unit.

http://www.allecoenergy.co.uk/newsl..._Updates/VPhase/VPhase_Instruction_Manual.pdf on pages 13-14 which also suggests that it might be contrary to G83 to connect PV to the load side of a VO but I am not sure that this is a correct interpretation of the regulations.

http://apexvo.co.uk/wp-content/uploads/2012/06/ApexVO_Manual_Version_1_0.pdf on page 7
 

Reply to Over Voltage as SolarEdge SE3500 Error Code 33 Trips out frequently. 253v / 264v ? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hello, I have a EV charger that is reporting over voltage and is unable to charge. the charger will operate up to 253V The solar inverter reports...
Replies
6
Views
3K
Hi. Not sure if it's the right place to ask, so won't be upset if it gets removed. Apologies if the terminology (PEN/PME/etc) is used...
Replies
44
Views
7K
I (well, the MCS installer) obtained approval under G59 back in 2015 for 11.5 kW of grid connection on a single phase. 12kW of panels into two 6kW...
Replies
3
Views
1K
Hi. I have a UK customer that has an agricultural building that will have a Diesel TPN generator supplying a corn dryer electrical installation...
Replies
1
Views
1K
Hi, Similar'ish question to my other thread but little more info now so a different approach but sorry if duplication. UK, single phase. Just had...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top