Re: Over Voltage as SolarEdge SE3500 Error Code 33 Trips out frequently. 253v / 264v

it is contrary to G83 as the inverter would have no way of monitoring the grid voltage the other side of the VO unit, so while the voltage at the inverter would be fine, the voltage the other side of the VO unit would be say 18V higher than whatever voltage the inverter was seeing.
 
Re: Over Voltage as SolarEdge SE3500 Error Code 33 Trips out frequently. 253v / 264v

Yes, I understand that. But in those circumstances the inverter would only be outputing, say, 222V and I cannot see where in G83 it says this would be a problem? Perhaps there is a design issue with VO units and reverse current flow?

And possibly G83 itself needs an update to add a paragraph on VO.
 
Re: Over Voltage as SolarEdge SE3500 Error Code 33 Trips out frequently. 253v / 264v

Solaredge inverters can be set to UK230 or UK240 depending on the local grid voltage. They can also be updated remotely if a support ticket is raised with Solaredge Technical support.

If you're getting 245V from the mains it sounds like your inverter has been set to UK 230 and small transient spikes are tripping you off.

Contact the installer/DNO/Solaredge and see if you can have the inverter set to UK240 which will give you a bit more tolerance in the +10%/-6% range of voltages
 
Re: Over Voltage as SolarEdge SE3500 Error Code 33 Trips out frequently. 253v / 264v

Also as mentioned earlier, VO won't help you...

Your PV has to be connected at grid voltage i.e. 'before' any VO unit.
 
Re: Over Voltage as SolarEdge SE3500 Error Code 33 Trips out frequently. 253v / 264v

Issue now rectified ! :bulb2:
Thanks for folks responses. To let you know my issue was fixed when SolarEdge did a remote Software / Firmware upgrade on my SE3500 (via the Ethernet connection I suppose) I didn't get many details other than it should solve the problem which after a week of observation it apparently has. Pleased about that! I now see my supply voltage fluctuate between ~245 and 253V but it no longer causes the inverter to trip.
 

Reply to Over Voltage as SolarEdge SE3500 Error Code 33 Trips out frequently. 253v / 264v ? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock