Currently reading:
Paralleling conductors

Discuss Paralleling conductors in the UK Electrical Forum area at ElectriciansForums.net

overskilled

-
Mentor
Arms
Reaction score
314
Just bouncing something off people here..

Got a job on, customer currently has a single phase 230v 16Amp commando socket he wants changed for a 32A ( Seemingly has a few machines in mind with a larger than 16A draw but below the full 32 that he's considering buying in...hasn't decided which yet tho...)
Its currently supplied via 1.5mm2 6491X singles in plastic conduit (checked the book 4D1A, Ref method B and its good for 17.5Amps) run is sub 10 metres, but a pain in the backside to alter (heavy immovable stuff in the way for starters)
conduit is 20mm, so no way I'm going to pull 4mm2 or 6mm2 singles down there...and because of obstructions..I can't change out the conduit for bigger nor run another piece of conduit..
Socket has to go where its going.

So my only option it seems....pull in another 1.5mm2 line and neutral and parallel them (for some unknown reason the CPC is 2.5mm2 (who knows why...I didn't install it whenever it was done)...which should give me 35Amps so more than enough to cover matters...be a royal pain to pull it in more than likely...but with some extensive blue language...it should be doable. I don't especially like the idea...but I can't see any other way around the problem....

Anyone got anything to add that I've missed here?
 
One flaw in BS7671 compared with NEC is the lack of mention of fill ratio - i.e. 2 conductors in 20mm conduit has a much higher fill ratio and therefore less free air to dissapate said heat than 2 conductors in 25mm conduit etc...

Book is getting dumbed down bigstyle with worst case scenarios being treated as gospel rather than realistic scenarios...

Physics might not change but the figures given for the cables are lower than what they can carry (else half the street would going up in flames as the DNO cables ignite.....according to BS7671 those cables are all overloaded...)

Whats the actual sustained load on the circuit going to be..will that load be sustained long enough in all likelihood to cause a risk.

Anyone like to state how many circuits are running at 100% load constantly? (Without even mentioning the heavy derating that BS7671 applies to CCA as a safety margin - 30C ambient rating is a joke, never yet been in a british house that was hitting 30C 18-23C, lower still up here in Scotland or Yorkshire :p )

Apologies if this comes across as cranky rather than debatory lucien, my head is pouding, feeling like death warmed up and the more I read, the more it seems that Euro regs are written to the point of making a joke out of the cable sizes...the usual nanny state rather than trusting sparks to make the right call on cable sizing and giving them (and expecting those entering the industry to use) the mathematical equations to work it out, instead we get treated like idiot savants and told to slavishly follow a set of charts that often has no bearing to reality...nor to cables that are smaller CSA by a sizeable margin than the tables are requiring that have been carrying a load as big or bigger for donkeys years and yet have no sign of thermal damage, IR test out ok - yet they are condemned because someone thinks we live in the subtropics, with ambient temperatures hotter indoors than the average Spanish home, drowning in insulation and with every circuit running flat out 24/7/365 - Then happily let 2.2Kw Kettles be sold with 0.75 or thinner flex on a 13A fused plug, ditto for hair dryers, straighteners etc...all of which are far more likely fire risks...especially with the massive amount of counterfeit cheapenese flex on the market....
Oh dear lord...I'm turning into Eng54... :lol:
 
One flaw in BS7671 compared with NEC is the lack of mention of fill ratio - i.e. 2 conductors in 20mm conduit has a much higher fill ratio and therefore less free air to dissapate said heat than 2 conductors in 25mm conduit etc...
I mentioned this in a thread not that long ago and I think it was Rockingit (apologies Rockingit if it wasn't you) that said there were stipulated permissible fill ratios in the BS7671 but they were basically just ignored.
 

Reply to Paralleling conductors in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top