davelittlewood

House build in mid 80's
Single Phase 240V installation with main supply board in exterior wall enclosure.
CU mounted in downstairs toilet in the middle of the house. Main tails length in excess of 7m.

1) During the installation of the house alarm the alarm fitter (Qualified Electrician) commented that the main tails to the CU were small.
2) If the cooker and extractor fan are running and then the kettle is turned on then the fan speed noticeably drops.

I have measured the drop in pd at the CU (21:30 tonight).
With almost no load = 242V
With ~4kW load = 237V.

(I guess that grid pd is up now as it's catching up with Sunday lunch load!)

Is a drop in 5V across the tails something that needs attention?

I'm well aware of Part P so I'd get a Qualified Electrician to actually replace the tails if needed.
Just looking for some advice.

With a drop of 5V across the tails, the power consumed is about 85W.

Any help appreciated.

Cheers,

Dave
 
I measured the pd at the main switch in the CU with and without load.
I guess it could be in the single phase supply to the house.
I'll do the same test at the main supply board at the side of the house
 
You're not measuring the volt drop across the tails by doing the tests you describe. The test would kinda moot, the wiring manufacturers publish volt drop figures for the wiring. If the tails are undersized just get them replaced.
 
The tails are actually T+E, can't get it in to see the writing on the sheath or measure directly but the overall width of the outer is about 20mm so from various tables I think that it's 16mm^2.

The house originally had 2 x 8kw showers, 7kW cooker + usual lighting and ring main circuits.
 
Are you sure that T&E is the tails? Is it not fed from - fuse or mcb in the main supply board you described? If it is fed from another board then that changes the situation
 
As far as I can tell it's T+E from the mcb on the main supply board all the way to the CU.
I can see the T+E leaving the mcb and coming into the CU.

It comes in from the top, curls round behind the main switch and then pops back up again.

IMG_1051.jpg
 
In which case, that isn't the tails. That is what is called a sub-main or distribution circuit.
Tails are the cables which connect between the meter and the main switch or first fuseboard.

A little bit of voltage drop when loads are applied is not uncommon in the suppliers distribution cables, especially on long cable runs.

Where I live it is quite normal to see the lights dim when the kettle is switched on as we are in a rural location on an overhead line from a small pole mount transformer.
 
That looks like 16mm to me, you mention an MCB at the main supply end, what is the current rating ? I'd be more used to seeing a switch fuse set up than a MCB at the source for a sub-main.
 

Reply to PD drop over tails to CU in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

As the user name states, I am not an electrician but I am trying to be an informed customer when dealing with a friendly local sparky and the...
Replies
18
Views
5K
hi This is just a starter because I haven't done any measurements yet (I was a guest there) and what I can do will be restricted as this has never...
Replies
10
Views
3K
  • Locked
Hi, we need some advice on our scenario with regards to our rewire plan. I will get this out of the way first... We are planning to put the house...
Replies
24
Views
5K
M
I am building a granny flat for my increasingly wobbly mother in our garden. All proceeds well so far except it has obviously cost more than...
Replies
3
Views
2K
T
Hi, First let me just say that I am not an electrician although in the past I've done the usual garage and shed wiring without having any...
Replies
24
Views
8K
Thai Amateur
T

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock