Sorry, yeah you're right, 80A fuse and switch.

I also want to run a 3kW single phase compressor in the garage (which is currently an unfused spur on the kitchen ring main) so I'm concerned that the 16 sq mm from the switch to the CU isn't up to it.

As I said, I'm not an electrician, hence the request for some advice before I start getting quotes to put in larger cable.

As the CU is right in the middle of the house it's going to be a PITA to get access to run the new cable.
 
Well this thread is taking a rapid change of direction isn't it.

We've gone from a concern over a bit of voltage drop to advice on how to proceed with a supply for a compressor!

I would be more concerned about the unfused spur than the 16mm submain.

You need an electrician to visit and make an assessment of what is needed and provide a quote.
 
A 7 metre run of 16mm T&E ought to cope fairly comfortably with the demand in an average home, the volt drop under fairly small loads does seem a little high though, that could be indicative of a poor connection anywhere upstream of your CU or a number of other things,might be nothing at all wrong even.
The 3kW compressor should be fine IMO, but ideally it would be better if the garage was on its own circuit, would that also be an awkward cable run from the CU ?
All things considered your best bet would be to get a decent electrician around to check it out properly and discuss the best course of action.
 
Last edited:
We're going to rebuild the garage (as the foundations are knackered) so I'm already planning to get a sparky to put in a dedicated circuit for the garage rather than the spur from the kitchen ring main.

Picky below of the board with the main switch, meter etc.
The mcb in the bottom left supplies a separate circuit for my car lift (this might end up being the circuit for the complete garage as it's over spec'd for the load. I asked the electrician to put in a larger cable just in case).

You can see the T+E leaving top left.

IMG_1055.jpg
 
With all due respect the supply job for your car lift looks a lash up , the supply to the enclosure looks like 6mm straight off the outgoing side of the house sub main switchfuse - and apart from the MCB in the enclosure bottom left of the photo there should be a proper DP isolator, depending on the cable run/when the work was done there should really be an RCD also.
 
With all due respect the supply job for your car lift looks a lash up , the supply to the enclosure looks like 6mm straight off the outgoing side of the house sub main switchfuse - and apart from the MCB in the enclosure bottom left of the photo there should be a proper DP isolator, depending on the cable run/when the work was done there should really be an RCD also.

The mcb is after the main switch so no other isolator is needed.
And SWA rarely requires RCD protection
 
But is it really good practice to have to isolate the whole house in order to properly isolate the other separate supply , the thoughts on RCD protection were based on what's at the other end but of course I haven't seen the other end of the SWA.
 
But is it really good practice to have to isolate the whole house in order to properly isolate the other separate supply , the thoughts on RCD protection were based on what's at the other end but of course I haven't seen the other end of the SWA.

It's no different to feeding it from a way in a CU.
DP isolation is only required for the main switch, after that single pole isolation is all that is required.

There is a car lift on the other end of it.
 

Reply to PD drop over tails to CU in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

As the user name states, I am not an electrician but I am trying to be an informed customer when dealing with a friendly local sparky and the...
Replies
18
Views
5K
hi This is just a starter because I haven't done any measurements yet (I was a guest there) and what I can do will be restricted as this has never...
Replies
10
Views
3K
  • Locked
Hi, we need some advice on our scenario with regards to our rewire plan. I will get this out of the way first... We are planning to put the house...
Replies
24
Views
5K
M
I am building a granny flat for my increasingly wobbly mother in our garden. All proceeds well so far except it has obviously cost more than...
Replies
3
Views
2K
T
Hi, First let me just say that I am not an electrician although in the past I've done the usual garage and shed wiring without having any...
Replies
24
Views
8K
Thai Amateur
T

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock