Following the tragic tale from @telectrix about lightning damage to phones and modem leading to a serious loss of beer money I decided to take a look at an el-Chepo SPD from Amazon to see if it looks worth considering. This one:
When it arrived the box looked somewhat aged, but that is not so important (might explain the low cost as excess stock?) seen here: phone-SPD-1.jpg
Somewhat bizarrely considering its purpose is is wrapped in an anti-static bag
phone-SPD-2.jpg
Otherwise looked like the sales photo and easy enough to get apart:
phone-SPD-3.jpgphone-SPD-4.jpg
The insides show a pair of 3-terminal gas discharge tubes on the 'In' side (connected to external phone line) to take the brunt of any surges, followed by 1 ohm resistors and some transient suppression diodes to clip the peaks of those firing in to conduction on the 'Out' side of the device (connected to your modem):
phone-SPD-5.jpg
PCB is cheap but of reasonable quality, but not sure quite how much of the GND area would remain after a 10kA surge:
phone-SPD-6.jpg
Overall it looks quite well made for the surprisingly low cost. Earth arrangement would need consideration though, as you want some short path to true Earth for the surge to go, but also you want your phone/modem not to have its CPC at many kV difference due to inductance and dI/dt of the surge being diverted. Maybe a 0.1uF capacitor of decent size / working voltage (class X style) between the earth for this SPD unit going to a nearby rod and the supply socket CPC of the modem/phone.

TL;DR Conclusion is it might save your phone for a couple of beers.
 

Reply to Phone line SPD on budget in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock