During a recent inspection on a 3 phase board I have some MCBs rated at 6KA
And some rated at 10 KA .
The ZE is about 0.04 to 0.05 depending on phase , form my calculations this works out to 9.95 KA ( I can only measure single phase pfc)
On a consumer unit we allow 16KA if its backed up by a BS1361
Does this apply to a 3 phase board or will a lot of MCBs need changing?
And some rated at 10 KA .
The ZE is about 0.04 to 0.05 depending on phase , form my calculations this works out to 9.95 KA ( I can only measure single phase pfc)
On a consumer unit we allow 16KA if its backed up by a BS1361
Does this apply to a 3 phase board or will a lot of MCBs need changing?