Search the forum,

Discuss r.c.d. tripping times ?? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

the operating current of the rcd is irrelevant for the 1xtest, it should still trip in <200/300mS whatever the rating. all you need to alter is the test current on your test equipment. i.e. 10/30/100/300/500/1000mA.
 
Rcd test for a 30ma trip
Is 1/2 15ma current should not trip
1x 30ma current should trip before 200milli secs
5x 150ma current should before 40milli secs
That is for 16th edition
So for 100ma rcd you still use 1/2 x 1x 5x
 

Reply to r.c.d. tripping times ?? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock