Discuss R1 + R2 expected readings in the UK Electrical Forum area at ElectriciansForums.net
Surely a bad connection is going to make BOTH readings off.Previously I’d do dead and live testing and I’d be able to check check the r1 r2 results by the zs readings
Yea I generat know what I’m looking at what seems high and things but I just wanted something to work towards incase I was been slightly generous and over cautious chasing faults that didn’t really need further investigation.For EICR purposes, the two things that come to mind are how close the calculated Zs is to the limit for the device, and a sense of how big the property you are in is and whether a reading seems plausible. The more you do the easier that gets.
e.g. if you're re in 2 up 2 down and you get 1.5 ohms for an immersion heater circuit then a bit of head scratching is due.
The other thing you can do is try RN+R2 or use a wander lead to obtain a 2nd frame of reference, and whether it's R1, R2 or both that have a loose connection.
I'm assuming that you are allowed to do Ze, Zs@DB and RCD tests, and your company only prohibits live Zs readings?
I do know the methods for carrying them and things,This is so basic for someone qualified. Whether dead or live testing, you should know the methods of carrying them out (and working them out) without thinking.
Yea we carry out ze and rcd testsThis is a 'modern' take on Zs testing that you don't do it live except for socket outlets where there is no risk of exposed live parts but as @timhoward asks do you carry out Ze and rcd tests.
Have you ever asked why seems like someone has carried out a risk assessment and deemed it is not safe.Yea we carry out ze and rcd tests
It’s just the zs we don’t carry out
@Lt1990 is only carrying out works in the way as suggested by his company.You are either going to be carrying Zs on lights or sockets principally. Spurs come into it as well. I always do live tests at sockets, spurs and lights. I use the lightmate by Kewtech for Zs test. On courses it has been put to me this is a Lim, as you have to go up a ladder and H&S forbid this in many scenarios. I just get on with the job and test it all. When I put the Zs reading for each circuit I like to be sure I did actually read it with my MFT, I can't imagine any other way to operate. Maybe I am missing something, but I don't think so. Convince me! I mean how do you fill in the forms? Yes calculation, but I am not convinced that is kosher. For instance you can find that there are big variances between R1/R2 + Ze calculation and Zs measured with an MFT.
Where I previously worked we carried out full tests but I’ve only recently started for this place and from what I can gather it’s literally just down to them not wanting us to work live.Have you ever asked why seems like someone has carried out a risk assessment and deemed it is not safe.
I agree with you they is differences from calculations and actually measured results and I use to always do live tests at previous companyYou are either going to be carrying Zs on lights or sockets principally. Spurs come into it as well. I always do live tests at sockets, spurs and lights. I use the lightmate by Kewtech for Zs test. On courses it has been put to me this is a Lim, as you have to go up a ladder and H&S forbid this in many scenarios. I just get on with the job and test it all. When I put the Zs reading for each circuit I like to be sure I did actually read it with my MFT, I can't imagine any other way to operate. Maybe I am missing something, but I don't think so. Convince me! I mean how do you fill in the forms? Yes calculation, but I am not convinced that is kosher. For instance you can find that there are big variances between R1/R2 + Ze calculation and Zs measured with an MFT.
Odd. There is working live and working LIVE.The place I work also tells us we are NOT to work live.
Dunno how the hell we're supposed to complete EICRs.
No someone has decided live not safe, simple as that.Odd. There is working live and working LIVE.
Originally I assumed that "working live" was the sort of high-risk activity such as making a change/repair to an energised system, you know the really squeaky-pants time and not something you would ever do unless there really was absolutely no alternative.
But of course any energised testing is also "working live" and then it gets more complicated as typically EICR and EIC both requier measurements such as Ze and Zs to be done, along with RCD trip-testing. Just how much exposure is too much to be safe?
- Do you base it on where you test (i.e. the CAT-II final point versus CAT-III DB location idea)?
- Do you base it on available arc-flash energy?
- Do you base it on whether it is done via probes or a 13A socket?
- If so do you leave light circuits untested, so the owner/occupier is the first one to encounter a problem?
Because they reckon that, nowadays, the average spark can't handle it, must be the explanation, In other words, more dumbing down of the trade.No someone has decided live not safe, simple as that.
Obviously.@Lt1990 is only carrying out works in the way as suggested by his company.
It’s an interesting discussion.The observation was more that there is no real life measurement for compliance with ADS and I conclude the risk associated with that is higher (unreasonable) (even within reg 14) than the reasonable test
Just shows you what matters with a bit of financial pressure. Frightened $hitless when it comes to a loss of profit. Actually, that's one of the main reasons for H+S, to prevent pay outs, but when it comes to the crunch, they gamble.I work a lot under some of the most insanely rigid health & safety rules imaginable. Don't want to go into details, but you couldn't make some of it up. Of course they forget all about those rules, when processes trump safety, and have you working in live busbar chambers.
Reply to R1 + R2 expected readings in the UK Electrical Forum area at ElectriciansForums.net
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.