Discuss Radial / ring fault in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
5
Hi everyone,
Hope everyone is keeping well.
At a property Fault finding prior to consumer unit upgrade.
Amazing that some bright spark thought it be a good idea to use the Cpc as a neutral And create a pen conducter.
Anyway,
Have a fault on a ring/radial circuit,
Tested end to end on what I thought was a ring, No continuity on any conductors, did IR test between both legs and all clear. So looks like it’s two radials, Or a separated/broken ring.
All IR tests are clear, And all ZS and continuity tests at all but two sockets Good,
Have two sockets that are are giving me 127V , and Although the CPC is visible at the socket, not getting any reading ( well getting greater than 2000) when testing to earth.
I’m thinking that the ring has been separated at some point and done badly,
Any advice on why I might be getting 127 vaults are two sockets for all of us are okay, been lifting floorboards and searching for dodgy junction boxes, but so far no luck.
Any thoughts would be helpful,
Thanks in advance
 

Reply to Radial / ring fault in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
485
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
290
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
479
Hi all, Gone to look at a intermittent ground floor sockets fault today, the RCBO was tripping at random times with no pattern. Nailed down a...
Replies
11
Views
1K
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
719

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock