Hello I you are all well
This is hard to explain but basically doing a three phase install and there is no power yet so I wanted to test two lighting circuits before the lifter went, I used an extension lead and connected live to phase L2 (that's what the lights were on) Neutral to the neutral bar and Earth to the earth bar (see attached picture) however the extension lead I was given had been wired with reverse polarity L-N switched so when powering on with all circuit breakers OFF one of the RCBOs blew up as it had a backfed neutral, power was quickly removed however has the integrity of all the RCBOs been compromised?
Thanks Lewis
This is hard to explain but basically doing a three phase install and there is no power yet so I wanted to test two lighting circuits before the lifter went, I used an extension lead and connected live to phase L2 (that's what the lights were on) Neutral to the neutral bar and Earth to the earth bar (see attached picture) however the extension lead I was given had been wired with reverse polarity L-N switched so when powering on with all circuit breakers OFF one of the RCBOs blew up as it had a backfed neutral, power was quickly removed however has the integrity of all the RCBOs been compromised?