RCBO trip when cabinet lights switch on

Discuss RCBO trip when cabinet lights switch on in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
3
Call out for tripped 20A RCBO on TT system, 3 Halolite T4 fluorescent cabinet lights (class 2) on 3A FCU from radial socket circuit, trips occasionally when lights are switched on.

Circuit tested including IR, all results good, RCBO tested including ramp test, all good.

Connections checked, all good.

No unexpected earth leakage shown with clamp meter on tails.

Can recreate the trip when all 3 lights are on, but turning any one off at its own switch so that only 2 are switched on / off via lightswitch the fault cannot be recreated.

Thoughts please.
 
Thanks for your thoughts so far....

lights are actually being used to illuminate understairs cupboard, so all cables / links visible and appear undamaged, no steam or moisture present.

Littlespark, I also assume / consider likely a cumulative effect of the 3 lights, but as should be able to link up to 6 on a smaller RCBO / MCB by manufacturers instructions I also assume that at least 1 may be faulty.

I am going to disconnect lights from the circuit and PAT test when go back and see if anything shows up, didn't have time for this yesterday.

Suffolkspark, will try FCU change as a cost effective "worth a go" before changing lights if nothing else "comes to light" - sorry about the pun!

Timotei
 
Just been back...

With benefit of more light (and glasses!) what I thought were ECP's on the lights were in fact plastic, so didn't pursue further testing there.

Lightswitch and FCU both good.

Gut feeling the lights are sound, and don't want to go replacing them only to have the same issue......so temporarily connected the circuit into another RCBO....unable to reproduce the fault.

So now thinking dodgy RCBO, depsite testing correctly on 0.5 / 1 and 5 x, plus ramp test 25mA.

It's a BG compact RCBO and I have read somewhere else on the forum that there have been issues with some of these, although I can't now find the relevant thread or remember specifically what the issue was.

Are there any further tests to try on the RCBO before trying a replacement?

Anyone able to tell me anymore about the BG compact RCBO "issues"?

Timotei
 

Reply to RCBO trip when cabinet lights switch on in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top