Discuss RCD failing ramp test. x1 and x5 both OK in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
2
Testing an Ashley & Rock BS4293 RCD Type AC (CU dated 1989, property built c. 1990-91) this morning with a Metrel 3152 on RCD Auto; x1 and x5 were both satisfactory, but the ramp test failed to trip. I tested a few times at both a socket outlet and the RCD terminals with the same outcome. Any suggestions other than replacement or is that my only option?
 
Genuine earth leakage from one or more circuits giving a false baseline, try testing at the RCD terminals with all circuits isolated then flick them on one ate a time until the culprit is found.
 
I've had it once where the 4 tests that did trip each shook the device a little and by the time of the ramp test the connection was loose on the bus bar. The tester would probably fail to test if that were the case though.

As above, confirming that a ramp test at the terminals with no load also fails would be good.
Does test button work? Do x1 tests still trip it?

I'm idly wondering about DC leakage even though that apparently didn't affect x1 and x5 tests.
 
I've had it once where the 4 tests that did trip each shook the device a little and by the time of the ramp test the connection was loose on the bus bar. The tester would probably fail to test if that were the case though.

As above, confirming that a ramp test at the terminals with no load also fails would be good.
Does test button work? Do x1 tests still trip it?

I'm idly wondering about DC leakage even though that apparently didn't affect x1 and x5 tests.
Tests were carried out with at both a socket and then again at the terminals with all MCBs off - same result
 
Only because I've done it myself, have you checked the MFT is on the right setting?

I've had it on 10mA before now, in that case the 1x and ramp 'failed.

If so it's looking at a new RCD..
 

Reply to RCD failing ramp test. x1 and x5 both OK in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Morning everyone, this is my first post - although i had an account years before that seems to have been lost. Can any of you shed some light...
Replies
24
Views
5K
Doing one more of the flood of EICR today on a rented property before a tenant change, but ran into a slightly interesting case so would...
Replies
71
Views
13K
Folks, A bit baffled (not difficult) ... added a light switch in a rental this week (empty property so no social distancing issues) and checked...
Replies
15
Views
3K
I know how I was taught to test a RCD, 6 tests in all two no go, two under 300 mS and 2 under 40 mS with no load. But thinking about it not so...
Replies
7
Views
3K
On completion of some recent minor work , I carried out the usual testing and noticed the incoming 100A 30mA rcd on the Consumer unit was failing...
Replies
33
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock