I was looking at that aswell, didnt investigate, you think that has something to do with it? RCD should still trip on test right?
 
I had this lastnight - went to a house - RCD tripping on split 2.
Tested split 1 and no trip upto 550mA

Hit the test button and then ramped it again - tripping at 10mA now - RCD replaced


Tripping at 10mA??
You sir have replaced a faulty RCD with another faulty RCD
Anyway to the op have you ramp tested the faulty RCD yet?
 
no, will do that. RCD seems fine though. I'm gonna look into that earth reading from 1st floor sockets though, didnt get chance to yet
 
so..once youv sorted out your end to ends....you can just jolly well go round the points again on that circuit for a real value of (R1 R2)....cant you...

- - - Updated - - -

this is sounding more and more like the same old farce....
 
well i noticed the readings from 1st floor sockets were strange, and someone else pointed it out here just few mins ago....

L-L 0.79
N-N 0.79
E-E 0.52
 

Reply to RCD not tripping on test in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock