Currently reading:
Rcd protection office sockets

Discuss Rcd protection office sockets in the Commercial Electrical Advice area at ElectriciansForums.net

ses

-
Reaction score
118
Hello chaps

Got an office job where we are rewiring 3 stories with surface mounted trunking and double sockets for Computers etc

New amendment has done away with under supervision of skilled or instructed persons

The company does not have a policy in place to tell staff not to bring in their own personal items so a risk assessment will not suffice as omission of rcd protection.

Whats the best method without bankrupting me or the client to install rcd protection.

Approx 45 double sockets across 3 floors

5 for dedicated equipment servers etc

So between 12-15 sockets per floor for Computors phones etc

Two rings a floor 7 sockets on 1 rccbo

Or 3 rings a floor 3-4 sockets per rccbo

Or 40 double rcd sockets looking quite expensive
 
How expensive would it be for the firm to lose a full circuit of computers and possible servers - Staff down time, lost work etc I bet if it occured once it would easily cover the expense of fitting RCD sockets provided the cables themselves are not subject to rcd requirements.
 
Don't forget the Leakage problems associated with such an installation
 
Our LA spec used to be 6 doubles per circuit on a 32A RCBO for general computer use. This was seen as a maximum for earth leakage nuisance.

The dedicated use sockets for your servers etc I would definitely leave non-RCD protected if the cable route permits.
 
Yes servers and printers will be on non rcd sockets and circuits

Pete999 yes the earth leakage is the reason I am asking what people think is the best/halfway solution to avoid tripping
 
Offices that I've just completed had a free standing raised floor access system with floor box sockets. We designed it to no more than 8 computers to one circuit. 32A rcbo with 4mm hituff under the floor on tray with a separate 4mm cpc back to the board from the Last socket for high integrity earthing.
 
Last edited:
Thats not so bad then

I could split the floors into two rings with 7-8 sockets ring

Are you classing a computor as one workstation i.e computor montitor, tower and phone?
 
Servers would be best put on labelled dedicated circuits and outlets without RCD protection. 'Turned pin' 13A sockets or commando sockets could be used to prevent unauthorised use
 
You can get cheap and cheerful unswitched RCD sockets for about £12.

I would tend to do a risk assessment of socket use for each circuit and see if some circuits can have RCBO protection, if not then go for the RCD sockets.
 
All sockets are pretty much for desk use so monitor, tower phone and possibly charger

Server and printers on dedicated circuits

All cables in trunking surface mounted

Looks like rcd sockets to be safe knightsbridge or bg nexus
 
The problem is that the spec is one double socket per desk
Then a surge protected extension with equipment plugged into it

Theres no policy to stop staff plugging there own items into this lead
 
The building is being knocked down in 4 years so the client is having a cheap and cheerful job to stop trailing leads as currently floor sockets all over the office floors
 
Hi,
You don't want cheap surge protection in the desk socket, it will be weedy and possibly a fire risk if there is a voltage problem. If you DO need surge prottection fit the propper stuff at the distribution board.
 
The client is reusing existing leads and equipment we are just installing new sockets and cabling

I will however mention your comments
 
The ups is 15minute backup

It tech is not in house

If the servers went down before the it department realised then that could be a problem
 
So what do they do when they have a power failure !
The servers will be just fine.

Just divide circuits up.
If they wanted a 24/7 uptime system then he will have to spend lots of money.
 
So what do they do when they have a power failure !
The servers will be just fine.

Just divide circuits up.
If they wanted a 24/7 uptime system then he will have to spend lots of money.

When they have a power failure everything goes off. If an rcd protecting the servers suffers a nuisance trip then the servers go off but everything else stays on.
There is a big difference between the two scenarios!
 
I don't see why you are trying to go out of your way to omit the RCD?
Why do you think that plugging in a server the RCD will suddenly become unstable and keep tripping!
When was the last time your computer at home operated your RCD? im willing to bet never unless it has a fault.
 
I don't see why you are trying to go out of your way to omit the RCD?
Why do you think that plugging in a server the RCD will suddenly become unstable and keep tripping!
When was the last time your computer at home operated your RCD? im willing to bet never unless it has a fault.

It doesn't have to keep tripping, it only has to do it once to cause a problem.
 
The server will be feed from a socket, and that socket will need RCD.

Whats the big difference Dave? Server goes off, server gets put back on when power is restored !
Where is this big nuisance problem coming from?
 
The server will be feed from a socket, and that socket will need RCD.

Whats the big difference Dave? Server goes off, server gets put back on when power is restored !
Where is this big nuisance problem coming from?

The socket doesn't need rcd protection of it is installed for a specific piece of equipment!

The big difference is that in a power cut everything and therefore everyone stops working and liability could be placed with the dno.
If the server goes off but all workstations stay on then everyone still stops working and the liability could lie with the person responsible for such a bad design.

Why are you so dead set against putting a server on a non-rcd supply? It doesn't need rcd protection so why would you install it?
 
Chaps

Thanks for all the comments and help

Theres no point arguing about rcd protecting a server or not

If you want to then no problem
If other people dont but it complies then no problem either

Dedicated sockets labelled up can omit rcd protection
 
Not aware that there has been a change in the requirements which now require sockets intended for a specific item of equipment to be provided with RCD protection?
Perhaps someone can quote the Regulation which now requires all sockets to be provided with RCD protection?
 

Reply to Rcd protection office sockets in the Commercial Electrical Advice area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock