Currently reading:
Rcd protection office sockets

Discuss Rcd protection office sockets in the Commercial Electrical Advice area at ElectriciansForums.net

There's not Spin, but my point was regarding plugging a server into a general socket with RCD protection.
There seems to be a switch in people's heads that as soon as the word "server" is mentioned they run around like headless chickens and the world as we know it will end.
 
There's not Spin, but my point was regarding plugging a server into a general socket with RCD protection.
There seems to be a switch in people's heads that as soon as the word "server" is mentioned they run around like headless chickens and the world as we know it will end.

No switch, just an obvious case of poor installation design
 
Yes servers and printers will be on non rcd sockets and circuits

Pete999 yes the earth leakage is the reason I am asking what people think is the best/halfway solution to avoid tripping
not my regs with me (in hospital) but there are a design for rings and radials,where leakage is an issue, sorry I can't point you in the right direction but it's in there somewhere
 
I did have a look but couldnt see anything other than circuits should be designed to limit tripping on rcds and about high earth leakage having dual earth path
 
I did have a look but couldnt see anything other than circuits should be designed to limit tripping on rcds and about high earth leakage having dual earth path

I think the accepted maximum earth leakage associated with a PC is 3.5mA for design purposes. In reality it will be lower than that, but also factor in that in reality a lot of RCDs will trip a good bit lower than 30mA.
 
I remember reading that equipment that is designed to be on a plug top the maximum permitted earth leakage is 3.5mA. Any equipment that produces more than 3.5mA should be hard wired. Ill try find it.
 
Last edited:
I'm not anti RCDs, all my 240V cutting tools have had RCD plugs on them for years.
However there does seem now to be this belief that nothing is safe now without one.
The fact is, the Regulations deem them to be just another form of additional protection.
One I might add,that is not acceptable for cables concealed above ceilings or below floors.
One of the problems, is that they require the test button to be operated every 3 months, and I don't know of anywhere where that happens.
Another, is that the 30mA required by the Regulations, is only really suitable for persons of average build and height, with good health. Even then they will not safeguard against other effects which an electric shock can cause, such as falling from a ladder or chair.
Their primary use is for mobile equipment where damage may occur to flexes.
They are not really necessary for fixed appliances such as washing machines, fridge freezers or even servers, which is why there is an exception for such in the Regulations.
They are not ideal for any item of equipment where the intention is to leave it constantly energised, as the test button needs to be operated every 3 months.
I am very anti this new requirement for a documented Risk Assessment.
We have Statutory Legislation, requiring employees to be either safeguarded against dangers electricity may present, or provided with training or supervision to safeguard against such dangers.
This new requirement is effectively calling our clients liars and criminals, requiring them to furnish us with a document stating that they will comply with statutory requirements.
 
I remember reading that equipment that is designed to be on a plug top the maximum permitted earth leakage is 3.5mA. Any equipment that produces more than 3.5mA should be hard wired. Ill try find it.

543.7.1.201 Equipment having a protective conductor current exceeding 3.5 mA but not exceeding 10 mA, shall

be either permanently connected to the fixed wiring of the installation without the use of a plug and socket-outlet or

connected by means of a plug and socket-outlet complying with BS EN 60309-2.
 
543.7.1.201 Equipment having a protective conductor current exceeding 3.5 mA but not exceeding 10 mA, shall

be either permanently connected to the fixed wiring of the installation without the use of a plug and socket-outlet or

connected by means of a plug and socket-outlet complying with BS EN 60309-2.

That is the one.

Not sure what size these servers are, but every rack/server we install is on a 32 amp commando plug/socket because I prefer not to use RCD protection for these.
 

Reply to Rcd protection office sockets in the Commercial Electrical Advice area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock