Currently reading:
RCDs and the Importance of the Test Button.

Discuss RCDs and the Importance of the Test Button. in the UK Electrical Forum area at ElectriciansForums.net

telectrix

-
Mentor
Esteemed
Arms
Reaction score
67,274
done a small job today. just a socket & SFCU ( for a light) in customer's shed, on existing feed. feed cable is 2.5mm on a 16A MCB, RCD protected. cable tested OK, installed bits. Zs 2.4Ω. ramp test of RCD, mft reads>51mS. prerssed test button on RCD (which the customer said had never been done or RCD tripped in 15 years). then re-tested. ramp 27mS. times... 32mSec@ x1. 9mSec@ x5. just goes to show that they can get sticky.
 
done a small job today. just a socket & SFCU ( for a light) in customer's shed, on existing feed. feed cable is 2.5mm on a 16A MCB, RCD protected. cable tested OK, installed bits. Zs 2.4Ω. ramp test of RCD, mft reads>51mS. prerssed test button on RCD (which the customer said had never been done or RCD tripped in 15 years). then re-tested. ramp 27mS. times... 32mSec@ x1. 9mSec@ x5. just goes to show that they can get sticky.
yes....
and how many customers take any notice of the test quarterly sticker....or are shown functional operation on handover...
 
Has anyone seen the article on RCDs in the ESC swtched on mag , ESC takes a look at adequacy of RCD main contacts , it's amazing what damage can be done with high fault currents to these contacts , something to consider about the quality off them !!!
 
Has the shed got its own board with an exported dno's earth? Lol

unfortunately, no to the 1st. and yes to the 2nd. shed is fed with a 2.5mm T/E in plastic flex conduit direct from MCB in CU. it's been there for 18 years, and the job was " stick us a socket and a light on that, mate". " as long as it tests OK" was my reply.
 
HI,
The Company I used to work for had us pressing the test buttons on RCD's on over 200 sites every 3 months ( as per manufacturers instructions ). Needless to say we integrated this with other maintenance work. Once a year we tested the tripping times of the RCD's and tested the button last. As Tel says they can get a bit 'sticky'.

Regards.
 
interesting point here....
if...lets say you were on a practical examination for the (now defunct) 2391...and you performed RCD testing at X1/2, X1 & X5...but then did not perform the manual test by use of the devices test button then the lecturer should be noting it against you...
same as the written part of the course....
when asked how to perform testing for disconnection time on say a 30mA RCD ...and you reel off the sequence of tests correctly...but then fail to mention testing by means of the manual test button....there will be marks lost for that...
a typical 1 mark question would be :
how many tests are required for a 30mA RCD to BSEN61008....candidates stating 6 would not get the mark....
 
Last edited by a moderator:
I've come across many RCD's that fail on disconnection times and on a leakage current ramp test but then the pass after operating the test button a few times.

Surely if the customer isn't pressing the test button periodically then the RCD should be replaced if it fails tests before the button is operated because it's failing in real life conditions and even if it passes eventually after the test button is pressed, in reality it will not meet disconnection times again after another few months of nobody touching it.
 
agreed. but the problem is that then thousands of RCDs would be condemned. just because manufacturers instructions were not folloewed.
 
I've come across many RCD's that fail on disconnection times and on a leakage current ramp test but then the pass after operating the test button a few times.

Surely if the customer isn't pressing the test button periodically then the RCD should be replaced if it fails tests before the button is operated because it's failing in real life conditions and even if it passes eventually after the test button is pressed, in reality it will not meet disconnection times again after another few months of nobody touching it.
if the RCD fails to operate 1st time using the manual test button then i was always told it should be condemned...but as has been pointed out....thousands of RCDs would then have to be condemned....a few goes usually loosens em up....
another one as well is an RCD should be replaced everytime it clears a fault....
suppose that puts testing them out to grass then....
 
bloody hit and miss. either they work or somebody gets fried. who's responsible? sparky who tested it 6 months ago or the manufacturer?
 
I was told on a recent 2395 course to test the rcd's before pressing the manual test button and one of the reasons amongst others of doing it in that order was that it could influence the test results. That argument could be difficult to prove or disprove I suppose.
I was told the same, I think it was on my 2330 - the sequence of tests (in order) should be:
x1, (both sides) x5 (both sides), x0.5 (both sides), push test button, optional ramp test.

As you say, then you can't 'influence' the results by warming it up by pushing the test button, and having already been tripped several times by the time you come to do the x0.5 test it's less likely to hide any 'nuisance tripping'.
I heard of an electrician who went to fail an rcd in a stage installation and was told "yes it will have failed - rcds need to be warmed up", suggesting you need to pre-empt when the fault will be and go in and warm up the rcd beforehand. I would have said 'warming it up' quarterly (or as a worst case scenario, annually) as recommended should be enough.
 
This rcd fail issue is a clear explanation as to why relying on Rcd's is fundamentally wrong, the things should be banished, a better approach needs to be sort. RCDs only give a false sense of security. The manufacturers would dissolve all responsibility as they would say that their instructions had not been followed.
Whilst I agree that after several manual trips the things work within specified parameters, they should be replaced. Perhaps the manufactures should employ quarterly rcd testers. Either that or every one that fails should be returned for a free replacement.
 
This rcd fail issue is a clear explanation as to why relying on Rcd's is fundamentally wrong, the things should be banished, a better approach needs to be sort. RCDs only give a false sense of security. The manufacturers would dissolve all responsibility as they would say that their instructions had not been followed.
Whilst I agree that after several manual trips the things work within specified parameters, they should be replaced. Perhaps the manufactures should employ quarterly rcd testers. Either that or every one that fails should be returned for a free replacement.
agreed....if you cant get a compliant Zs without RCD then theres something wrong....i`v seen several previous schedule of tests now when on an ECR with 1667 scrawled down the loop boxes.....not acceptable to me as its supposed to be additional protection on TN...i wouldn`t accept it for fault on a TN....which is effectively what it`s doing if Zs hasn`t been met without it...
 
HI,
The Company I used to work for had us pressing the test buttons on RCD's on over 200 sites every 3 months ( as per manufacturers instructions ). Needless to say we integrated this with other maintenance work. Once a year we tested the tripping times of the RCD's and tested the button last. As Tel says they can get a bit 'sticky'.

Regards.

Ha I do this on a couple of sites...just walk round the site pressing the buttons, nice and easy...
 

Reply to RCDs and the Importance of the Test Button. in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock