If you have circuits run in metal trunking (with cpcs) you don't include the trunking when determining/recording the cpc size...
If you have circuits run in metal trunking (with cpcs) you don't include the trunking when determining/recording the cpc size...
SWA sheath is no different if you are using a core as cpc
Why would anyone be bloody daft enough to include a CPC in earthed trunking
Why would anyone be bloody daft enough to include a CPC in earthed trunking
?? lol!!
Why would anyone be bloody daft enough to include a CPC in earthed trunking containment system?? lol!!
Is that right eng, u should include a cpc if only for good working practice. What happens if the trunking continuity fails! We'll all be buggered if we scrimp on safety. Lol!!!
And the reg that tells you not to?
Not saying you have to include it in the CPC size above the cable conductor CPC size but there is nothing stopping you using it ...... reg 543.2.1
Is that right eng, u should include a cpc if only for good working practice. What happens if the trunking continuity fails! We'll all be buggered if we scrimp on safety. Lol!!!
But you could say the same about cpc cables...
The benefit to using trunking as cpc is the very favourable R2 values you achieve, to add cable cpcs is just a waste of time, money and the world's resources - don't you care about the environment??
Also, all you will achieve, is filling up the containment systems with pointless CPC's, that can't come close to matching that of the containment system they are enclosed in!!
If you are still arguing that you can combine a copper CPC and a steel CPC to make up the required minimum CSA you are WRONG!! Which ever one you do choose, it must be capable of taking the full fault current on it's own, not as a combined entity. A fault will always choose the easiest route to earth, so it will be the copper conductor (with superior conductivity) that will take the hit in a combined copper/steel arrangement!!
What would you know about ''Good Working Practice''?? lol!!
Ive been to conduit and trunking jobs with no cpc that suffered with poor zs, if there had been a cpc this wouldn't have happened. So you do it your way eng and I'll do it mine, ok.
Looking at the part of my post you highlighted, then your reply, I am guessing you perhaps 'speed read' it lol
Have to disagree with you there.
A fault current will split itself between the two with a ratio depending on resistance of the conductors. It will not all just flow down the one conductor. The steel has an equivalent copper x-sectional area (less than copper because its resistance to current flow is higher) so provided the two together meet the minimum x-sectional area required for the fault you satisfy the requirement.
That is my understanding of why reg 543 permits the mixed use of conductors.