Discuss regarding supply for a fire panel. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

P

poolsharkuk

hi guys,
I hope im in the right place to ask these questions. (im a newbie to forums)

I have been asked to fit a double pole isolator from a dedicated supply so a fire company can fit a fire alarm system.
would this be certified on a regular EIC or would I have to use a some other certificate, I am only fitting the spur.

all the best, hope someone can advise.
 
Cable run will need to be Enhanced FP200 or pyro. Can`t see it being larger than standard 1.5mm 2c & E Fused spur you can buy off the shelf, by Crabtree or MK.

3467mr_0.jpg
 
Supply should be in red FP200 these days, but standard EIC will suffice. Make it clear to the client that the fire company should provide the BS5839 paper work.
 

Reply to regarding supply for a fire panel. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Good evening! Don’t have a huge deal of experience with fire alarms but having to work on a conventional system at the minute with various...
Replies
8
Views
596
Hello People Our Enphase solar system needs to have the AC supply shut down via the fire alarm contactors local input output unit that has NO &...
Replies
0
Views
484
I am doing renovation to a cafe in Scotland at the moment and after speaking to the local council the building requires the minimum standard for a...
Replies
5
Views
1K
On this commercial building we are refurbishing it has the above fire alarm panel which I think is pretty much brand new, I'm not even sure it was...
Replies
6
Views
1K
Hi guys been asked to put a radial in for spurs for a fire alarm panel supply is it okay to use red FP200 to carry 230v? If so or not could you...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock