Search the forum,

Discuss Requirements for RCD protection in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
8
Good morning all. So question; if you’re making additions to an existing circuit, but the new cable is not min 50mm deep in wall or mechanically protected and the current circuit is not RCD protected do you tell customer that RCD protection is required as per the regs? My thought is yes and explain why it’s needed to customer; if they don’t want it then I’d walk away but just want to hear others views. TIA
 
So adding 3 new double sockets in to existing ring but one of the sockets in the wall cannot go 50mm deep. Oval conduit isn’t really mechanical protection.
 
Yep, there the option for that possibly. My post was really to answer a question I had with another spark about some work being done. My view was it needs either proper mechanical protection (metal conduit) or (a future proof measure) RCD protection.
 
For me, with the new regs I always where applicable advise customers about the need for RCD protection. Some jobs I win, some I lose as there’s always someone willing to just wire it up and then throw smoke.
 
I wonder what the scams view point is working on an older non rcd installation and not adding in any rcd protection..?
 
same as all of us.all new sockets added require RCD protection, even if the existing sockets are not. e/g. feed new sockets via a RCD FCU. if not protecting the whole circuit.
 

Reply to Requirements for RCD protection in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top