Discuss Ring final circuit Zs. in the UK Electrical Forum area at ElectriciansForums.net

Iona222

Trainee
Reaction score
41
Can you get the zs by using a earth loop impedance tester. I was taught if there's 2 rings circuits, you can do r1,r2, rn /4 on 1

On the other ring you can plug in the earth loop impedance tester and measure the zs. If you do it that way you must write in the observations you measured.

Have I been taught right?
 
Can you get the zs by using a earth loop impedance tester. I was taught if there's 2 rings circuits, you can do r1,r2, rn /4 on 1

On the other ring you can plug in the earth loop impedance tester and measure the zs. If you do it that way you must write in the observations you measured.

Have I been taught right?
2 methods.
the 1st one you mentioned is by calculation... (r1+r2)/4 = R1+R2 and Zs = Ze+ (R1+R2). this is generally for initial verification and eliminates live testing.

2nd method is more accurate as it is a direct measurement and takes into account parallel paths such as bonding etc..

Both should be done IMO and the readings entered on the EIC.
 
Can you get the zs by using a earth loop impedance tester. I was taught if there's 2 rings circuits, you can do r1,r2, rn /4 on 1

On the other ring you can plug in the earth loop impedance tester and measure the zs. If you do it that way you must write in the observations you measured.

 
Measuring all your little r readings is very useful because it A) verifies you actually have a ringadingding , and B) you can use these results later to calc your R1 R2 value.

once the circuit is energised you can plug in your efli tester to get your actual Zs reading

you should recorded all your values on the test sheet
 
As Tel says above; calculate then testing and compare.

Any idiot can press a button and wrote down a number, the skill comes in understanding the result, why/if the reading differs from the calculation and so on.

I don't know about everyone here but I like to know I should be getting, otherwise it's just ink on a page and has little meaning, bar filling box.

I had this same argument in college with the lecturer; I asked why are we not bring taught best practice, why they didn't find it necessary to go above the minimum requirement and just why they aren't challenging the ethos from the exam board of just doing the minimum.
 
One thing I like about the RFC is you can verify it at the CU end with your r1,r2,rn readings (spurs excluded, obviously). During installation the figure-of-eight test allows very good checking of the condition/quality of connections to every sockets as any that differ by any significant amount are either on a spur or duff.

Of course if you have just installed a radial and know the end socket then you can achieve most of the same by checking against your calculations R1+R2 (to compute Zs), Rn+R2 and R1+Rn (to verify L & N are very similar and E is in the expected ratio for T&E).

When people complain the RFC testing is "more complicated" than a radial they often overlook the fact it offers very comprehensive fault coverage and they are usually skipping the neutral verification, etc, of a radial to the same degree.

Measuring Zs at the socket is easy and gives you the final check, but not as precise a measurement and I find the no-trip readings of Zs on my MFT are a bit variable (OK, maybe I should have got a Megger...).
 

Reply to Ring final circuit Zs. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi so i am doing a test on sockets on a ring Final circuit for family member. Got my end to ends r1 0.62, rn 0.64, r2 0.97, identified opposite...
Replies
3
Views
2K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
1K
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
877

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock