Problem as above - is a disconnected earth wire in a socket sufficient to cause this? If so, I would like a brief explanation of the safety mechanism involved.
 
That fault sounds strange as a short circuit to operate the MCB would not cause the RCD to trip unless it were faulty, if it were a fault to earth the RCD would trip without the MCB.
For both to happen would indicate a double fault perhaps a neutral earth fault of high resistance in another circuit protected by the RCD that only causes it to trip when there is a very high current e.g. a short circuit on the ring.
 
there's also the scenario whereby a short circuit trips the MCB and , in tripping, the MCB, being single pole, applies a momentary imbalance to the RCD, causing the RCD to trip. had this a few times, usually on a socket circuit,
 
hust on a matter of terminology, david, it's a ring final. a ring main only applies to a supply circuit wired as a ring.
 
That fault sounds strange as a short circuit to operate the MCB would not cause the RCD to trip unless it were faulty, if it were a fault to earth the RCD would trip without the MCB.
For both to happen would indicate a double fault perhaps a neutral earth fault of high resistance in another circuit protected by the RCD that only causes it to trip when there is a very high current e.g. a short circuit on the ring.
Hi - is a disconnected earth wire a short circuit ?
 
nope. it's an open circuit. however, a dissed. cpc could perhaps short out to a live terminal if flopping about in the back of an accessory.
 
In one word - NO.

Is this a real fault or a college task?
Think the OP may be he seems a bit long in the tooth to be at college, hope you don't mind me mentioning that fact
hust on a matter of terminology, david, it's a ring final. a ring main only applies to a supply circuit wired as a ring.
Getting touchy in your old age Tel? you are correct of course, but I thought I was the only person getting all vexed when people call a RFC a ring main.:eek::mad::p
 
Are you trying to find a fault and if so have you got the necessary test equipment or are you just disconnecting things and then resetting the RCD/MCB? It sounds like you don't really know what you are doing. If this is the case can I respectfully suggest you get someone in who has test equipment or knows what they are as you are likely to cause permanent damage to the equipment or risk someone getting hurt in the long run if you do not find and rectify the the fault properly.
 
Think the OP may be he seems a bit long in the tooth to be at college, hope you don't mind me mentioning that fact

Getting touchy in your old age Tel? you are correct of course, but I thought I was the only person getting all vexed when people call a RFC a ring main.:eek::mad::p
i also refuse to call a henry or a dyson a hoover.
 
ours is a henry called 30 bob, coz a customer was throwing it out, so i had it . all that was wrong with it was the 2 pole on/off rocker switch. replaced for £1.50.
 
Hi - can you confirm a few things? What is the mcb rating, was anything working when it first tripped? (Any holes drilled or screws put in wall lately :) ). With all appliances / lights unplugged / off does the mcb set normally, or is this an ongoing problem?
 

Reply to ring main mcb & main rcd tripping in the The Welcome Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock