Hello guys,

It’s my first post here so please be gentle :)

I’m having a kitchen extension done and will have the hob and few powerpoints installed on the kitchen island meaning the wires will need to run under the floor.

The floor is concrete subfloor and will have 80mm PIR insulation followed by underfloor heating and then 60mm liquid screed so pretty much standard build.

My question is what is the best placement for running the wires and do they need derating?

Thank you
 
I would run either 2 x 25mm flexible conduit or 1 x 32mm
under the concrete slab
put a draw wire in and let the electrician draw in the cables they need.
 
I would use a twinwall duct or may be 2 either 50/40 or 63/50 on the subfloor with the insulation over it which will hold it in position when pouring the concrete screed
Better to have too much duct capacity than find you don't have enough when the job nears completion
 
Damn, the
I would run either 2 x 25mm flexible conduit or 1 x 32mm
under the concrete slab
put a draw wire in and let the electrician draw in the cables they need.
builder just poured a new slab only last week, I guess I will have to chase the channel out for the ducting. Is there any min depth this needs to be at? Thanks
 
The ducting can go on top of the slab and between/under the insulation, but it will derate the cable's current carrying capacity. Whether this requires a larger cable is one for the electrician to decide.
 

Reply to Running kitchen island cooker wire in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi all. I'm currently building an island in my kitchen which will contain a gas hob. I've cut a trench about 60mm wide from the edge wall to...
Replies
16
Views
1K
We are installing a new kitchen and the electrician has supplied the electricity under the base units, there is a spur for a socket that will be...
Replies
4
Views
4K
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
835
Hello all, I'm renovating my kitchen and had a question about running wire around ductwork. In attached pictures - I need to have a receptacle...
Replies
0
Views
907
Hi All, We have an old Country villa in Spain. The housing electrics were not good so the house recently has been completely re-wired to a good...
Replies
2
Views
734

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock