Thanks Davesparks, that had been my preferred method if at all possible. As luck would have it, I spoke with a friend who works for the local DNO and he has confirmed exactly what you have just mentioned. I also spoke with another friend who has some 4-core 16mm SWA and 110mm twinwall ducting as an off-cut (he works on large private network installations and 25m is an "off cut" for them. I know the ducting is a bit over kill, but it's free, so why not!?

My intention is to use a none RCD protected MCB currently in the CU, utilising the 16mm SWA to supply an RCD-protected, small garage type consumer unit with a MCB for the sockets, and a MCB for the lighting. I will use the 3rd core as suggested. Hopefully I can take the SWA straight to the house CU, but I have a feeling that I will need to terminate the SWA and continue the supply in T+E back to the CU. Unfortunately, the house's CU is back in the centre of the house in an understairs cupboard.

It's staggering that the myth about sheds and PME/TNCS still persists.

Working on rolling stock, I have never really had much need to investigate this myth, I just remember hearing it mentioned on these sorts of forums in yesrs gone by.
 
My intention is to use a none RCD protected MCB currently in the CU, utilising the 16mm SWA to supply an RCD-protected, small garage type consumer unit with a MCB for the sockets, and a MCB for the lighting. I will use the 3rd core as suggested. Hopefully I can take the SWA straight to the house CU, but I have a feeling that I will need to terminate the SWA and continue the supply in T+E back to the CU. Unfortunately, the house's CU is back in the centre of the house in an understairs cupboard.

[\QUOTE]

Converting to T&E may put you back at square one with the need for an RCD for the submain depending on how it is installed/routed.

The 'best' way to do it, in my opinion, would be to run the SWA back to the CU location and fit a switch fuse to protect it rather than an mcb.
 

My thoughts exactly Dave. The more I look at the cable route through the house, the more I think it will be difficult. Unfortunately, the downstairs floor is solid concrete though. I should be able to SWA right up to the external wall and then terminate in to an IP box and run T+E under the upstairs floor and back down to the top of the cupboard where the CU is located. I am able to install it in trunking/conduit.

Alternatively there is a redundant piece of SWA which runs from the adjacent wall to the C.U., across the garage ceiling joists, down the side of the garage, under the decking to an outside IP box to provide a supply to the conservatory (I don't know why they did it that way either, so don't ask!!) That's now redundant now the conservatory is on the ring, so I could potentially use that, depending on it's size, integrity, etc. but it's routing is not ideal (looks like it's just chucked straight under the decking!)

I shall investigate further when I'm home, and let you all know the outcome/finished product.
 
Basic requirements for earthing and bonding
Where an installation serves more than one building, main protective bonding is required in each building served, except for a building where there are no extraneous-conductive-parts, such as metallic water, gas or oil installation pipes (Regulation 411.3.1.2 refers).

Option 1: Extending the earthing and bonding system

supply_to_a_detached_outbuilding_1.png


The image shows an example of the earthing and bonding arrangements where the installation in a house is extended to serve a detached outbuilding. A Building Earth Marshalling Terminal (BEMT) is usually provided in the outbuilding to marshal together the main bonding conductor(s), if any, and the circuit protective conductors (cpcs) in that building. The BEMT must be connected to the MET by:

• the cpc of the distribution circuit supplying the outbuilding, and

• a main bonding conductor, if there are any extraneous-conductive-parts at the outbuilding.

As shown, the functions of the cpc and main bonding conductor (if any) may be combined in a single protective conductor having a cross sectional area (csa) meeting the requirements for both functions.



Option 2: Making the installation in the detached outbuilding part of a TT system with its own installation earth electrode and MET

supply_to_a_detached_outbuilding_2.png


The image shows an example of the earthing and bonding arrangements where an installation in a house supplies an installation in a detached outbuilding, forming part of a TT system with its own installation earth electrode and MET. It is desirable for there to be no connection between the earthing and bonding arrangement of the installation in the outbuilding and that of the installation in the house (such as through a protective conductor or shared metallic pipeline), as shown.

Note: Although both options show an earthing facility provided by the distributor being used as the means of earthing (TN-S or TN-C-S system), the earthing conductor could be connected to an installation earth electrode instead (TT system).



Table 1 – Sizing requirements for cpc and main bonding conductor

supply_to_a_detached_outbuilding_3.png


Note. The requirements of Regulation 544.1.1, referred to in Table 1, can result in a main bonding conductor size greater than that of the live conductors or cpc of the distribution circuit supplying the outbuilding, particularly where PME conditions apply (TN-C-S system).

Table 1 summarises the requirements of BS 7671 for sizing the cpc and main bonding conductor to the outbuilding. If the functions of these two conductors are combined in a single protective conductor, this must have a csa not less than that required for either function. Where there is no such connection, the main requirements of BS 7671 applying to the earthing and bonding are as summarised in Table 2.



Table 2 – Requirements where the outbuilding installation forms part of TT system with no connection to the earthing and bonding arrangements of the house installation:

supply_to_a_detached_outbuilding_4.png
A further consideration applies where there is a connection between the earthing and bonding arrangement of the detached outbuilding and that of the installation in the house, if the latter installation forms part of a TN-C-S system where PME conditions apply.

Where this is the case, PME diverted neutral current may flow in the connection between the two earthing and bonding systems. To avoid harmful thermal effects caused by this current, the csa of this connection and of the main bonding conductors and the earthing conductor of the installation in the outbuilding needs to meet with the requirements for a main bonding conductor of the installation in the house (which are summarised in Table 1).
F me! did you swallow the reg's book!:)
 
I should be able to SWA right up to the external wall and then terminate in to an IP box and run T+E under the upstairs floor and back down to the top of the cupboard where the CU is located.

Just be aware that the T+E may need RCD protection, if you do it this way.
 
Just be aware that the T+E may need RCD protection, if you do it this way.

Am I correct in thinking that only RCD protection is required on the submain if it is in a wall and to a depth of 50mm or less? I can mechanically protect the run with galvanised trunking or similar (straight run across the floor and then a short 600mm run down the wall to the CU. Just not sure if I can achieve the bend radius to get the SWA up the side of the house, in beneath the ceiling/floor void and then down the wall. I'll have a proper look when I'm home and see which methods are possible with regard to cabling.
 

Reply to Shed Supply on TNCS/PME in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'm looking to get the lionshare of a small shed wired before a friendly electrician does the needful. I'm a confident DIYer, but I would...
Replies
25
Views
1K
Hi guys, I have supplied my Shed with a 6mm SWA cable into a nice consumer unit. In there I have a 6Amp MCB for the lights and a 16 A supplying a...
Replies
25
Views
1K
Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Replies
13
Views
2K
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
718
I've wired some cable to a small 3x3 shed with 2 gpos, a 15a GPO, and a light. The shed is about 2m away from the house on a concrete slab. The...
Replies
0
Views
603

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top