Search the forum,

Discuss Shower circuit design supplies in the UK Electrical Forum area at ElectriciansForums.net

His point is the MCB can provide only fault protection (i.e. not overload as well) for the cable to fixed loads.

The fundamental aspect is the shower load is too much for the cable if it is thermally insulated. Changing the MCB is not going to alter that situation, and would only add another part that would be overloaded under normal operations.

So the real issue is the cable getting too hot due to thermal insulation? That may be hard to check [in any sane way] if you can't inspect enough to know the typical route. But if you can see sections and they show no sign of thermal stress it should be OK.

If it is a risk then the best option would be to replace the cable with a higher capacity one.
 
This is an issue doing periodics as in most situations it is not possible to verify the full installation method of the cable. According to Table 4D5 unless you can confirm Reference Method C can be applied then 6mm cable is undersized for an 8.5kw shower. That's how I read it.
 
This is an issue doing periodics as in most situations it is not possible to verify the full installation method of the cable. According to Table 4D5 unless you can confirm Reference Method C can be applied then 6mm cable is undersized for an 8.5kw shower. That's how I read it.
I don’t fully agree as for all you know the cable has been installed correctly during the original install.
If there’s no evidence of damage and the circuit has been in use for years as is the case with this situation (red and black coloured conductors) then it’s pessimistic to give it a potentially dangerous code without evidence of any danger present or potential danger.
That said I think the OP has indicated they has been alterations done to the original circuit.

I think that the reference method on an EICR which you record can be a bit pointless tho as you said, it’s sometimes impossible to verify, but we could end up applying that scenario to every circuit present including ring final circuits that may have the ccc below the required 20 amps minimum but I wouldn’t code that without evidence of thermal damage or insulation present surrounding the cables.
[automerge]1587121839[/automerge]
To be honest, if it’s ran up the pipe boxing (which is dubious) I’d be tempted to give it’s reference method as method B
 
Last edited:
if it's in soil pipe box then it's gotloads of free air around it, unless some muppet has fille the box with itchy-poo. i'd class it as ref. C.
 
so what about cables in the voids between floors.? surely these aren't B. i'd class then as in free air, unless clipped to joists, i.e C.
 

Reply to Shower circuit design supplies in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have had my kitchen rewired and plastered. I have had a 6mm t+e on a dedicated 32a circuit for a 60cm electric cooker. In hindsight, had i known...
Replies
11
Views
725
Good evening all, I’m currently part way through my apprenticeship and we are working on IB, IN, IZ and IT and volt drop today. And it got me...
Replies
4
Views
506
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
535
Hi, I have a book on domestic wiring which says that everywhere there is a change in current carrying capacity along a circuit there must be some...
Replies
3
Views
336
Strange on this, we are wiring an extension at the moment and I would like to 3 way the (currently 2 way) landing switch to the new bedroom so...
Replies
14
Views
730

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock