Discuss Shower circuit help in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
10
Hey guys , went to a job last night to quote for a new shower install ... After removing the old shower front , I discovered 2 X 2.5mm t&e instead of 1 6mm .. the current shower is 8.5kw and ran into a 40a MCB on RCD side of a split board .. no signs of perished cables or burning anywhere ... Just wandering if ok to go ahead and replace or offer a new circuit in 10mm .. ? .. ps .. don't throw the book at me please haha ..
 
basically you have 2 x 2.5mm cables in parallel. if installed ref.method C, that gives you a Iz of approx 50A, so with a 8.5kW load (36A) Iz>In>Ib. unconventional, bit can't see a problem, asuming that the load is equally shared between the 2 cables. tin hat ready.

edit: what rating shower is being proposed?
 
basically you have 2 x 2.5mm cables in parallel. if installed ref.method C, that gives you a Iz of approx 50A, so with a 8.5kW load (36A) Iz>In>Ib. unconventional, bit can't see a problem, asuming that the load is equally shared between the 2 cables. tin hat ready.

edit: what rating shower is being proposed?
Shower is 8.5kw .. Triton exite plus ..

Thanks ? I just wanted a second opinion as I've never seen it done like that before ..
 
and check if cables are buriedin itchy-poo in attic. that would derate the ccc by upto 50%.
 
You think they utilised an rfc to supply the shower? Why not run 6mm at the time.

id check there’s no sockets on the circuit as well.

is there an isolator before the shower?

very very strange.
 
You'll have to be very sure that the two cables are the same length/route.
 
If there is an option, I would likely run a new correctly sized cable. This install has questionable ccc due to installation method and cable lengths. And to me it smells like a short cut when it was originally installed. Just my personal view but other than our beloved RFC, any ccc that required 25mm or less should be realised in a single conductor (voltage drop considered separately:) ).
 
i had a full roll of 2.5mm on the van. nearest 6.0mm cable was 40 miles away, and the pub was opening in half an hour. no contest. ???. ( and i did give the customer the readings on a beermat).
 

Reply to Shower circuit help in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Shower circuit (40a mcb 10mm cable 8.5kw shower ) tripping after 5 mins RESET trips after 2 mins...changed shower /cable /isolator still tripping...
Replies
7
Views
569
Hi all, My question relates to the omission of overcurrent protection (specifically overload and fault protection) at the origin of an...
Replies
6
Views
2K
One of the oddest jobs I've ever had today. Called by a plumber I know who had attended after a leak through the kitchen ceiling from bathroom...
Replies
24
Views
6K
Reusing old shower circuit to supply bathroom electrics? Hi everyone, hope you’re all doing well. So this is potential plan, Working on the...
Replies
4
Views
2K
Has anyone had this experience or could offer advice please? I have a 9.5Kw shower, it is fed from the DB in 10mm T&E, a run of approximately...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock