Single phase to three phase converter?????

Discuss Single phase to three phase converter????? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

B

Bright.Spark

I recently looked at a job where a customer is turning his garage into a workshop and he wanted me to check the electric was satisfactary. The garage is fed by a 2 core 4mm SWA from the house with an earth pin outside the garage and a 4mm earth going to an rcd board. When the customer showed me what he would be doing I was shocked, he has bought lathes and CNC machines from a warehouse. The machines are all 3 phase and he only has a single phase supply. He seems to think you can buy a converter which you plug in and it converts single phase to three phase????? has anyone come across this before?

Secondly the machines are 7.5 horse power would a 4mm be capable of this load? Im tempted to put in a 6mm as he says the converter needs 30-40 amps to work?

Any ideas???? Also do lathes draw a high start up current?

Thanks guys.
 
Yes you can get single to 3phase converters.
They do rotary types and solid state types.
Do a google search.
As for the power requirements, you'll have to look at manufacturer's data sheets.
The 4mm² SWA may be adequate, if using only one machine at a time.
 
One machine at a time only. I just hope they’ve got dual voltage motors otherwise your looking at two stage inverters (even more losses). As for lathes there’re normally DOL, but with the inverter you can set a ramp up. If he’s bought all this gear he should be able to afford a 10mm 3 core SWA feed. But the inverter still limits it to one machine at a time. Unless he’s got very deep pockets.
Rotary converters are a bit pre-historic and not efficient.
 
I have just made a rotory converter and it works just fine. i could not find a static one that could provide me with 3p+n (also a bit pricey), however a star wired rotory converter worked fine. i have had to put it on a 40A "D" type so it don't trip on startup, I think mine is a 3Hp motor.

I have put in 10mm as i don't just run the lathe.

CNC kit is very touchy so a good static converter is a must, rotory would be no good for this job.
 

Reply to Single phase to three phase converter????? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top