Discuss Smoke alarm replacement in the DIY Electrical Advice area at ElectriciansForums.net

Col1920

DIY
Reaction score
0
Hi Folks.....I'm replacing hard wired interlinked smoke alarms with new battery interlinked ones. I disconnected old alarms and left the wires connected to cable connectors. My intention was to push these into the ceiling and position new alarms to hide this. Downstairs cable is 4 core, and upstairs has 2 cables....a 4 core and a 3 core. Upstairs cables are no longer connected to each other. I switched mains power back on and my lights have tripped. My question is, has this happened because I've broken the link and should the 3 & 4 core wires still be connected upstairs? I hope that all made sense. Any advice would be greatly appreciated.
 
First I’m assuming what you call “3 core” is what we would call “twin and earth”…. A live, a neutral and a bare earth wire.
The 4 core being actually “3 core and earth”

Just sorting out the terminology.

The twin and earth at the detector upstairs would be the supply from the lights. Best idea would be to find where this cable comes from and disconnect from that end. If not, make sure the conductors of the t&e are in separate connectors, not connected to anything else and enclosed in a box.



Nice place, Dundee. Of what I remember.
 
First I’m assuming what you call “3 core” is what we would call “twin and earth”…. A live, a neutral and a bare earth wire.
The 4 core being actually “3 core and earth”

Just sorting out the terminology.

The twin and earth at the detector upstairs would be the supply from the lights. Best idea would be to find where this cable comes from and disconnect from that end. If not, make sure the conductors of the t&e are in separate connectors, not connected to anything else and enclosed in a box.



Nice place, Dundee. Of what I remember.
Hi, Thanks for your reply. Yes T&E and 3 core & earth. I don't think I can find where the t&e originates but I will certainly have a look. The wires are all separated. I've attached 2 pics. 1st pic is upstairs, and 2nd is downstairs. The 3 core & earth I assume is the same cable linking the other smoke alarm. I don't understand why it tripped if they're all separated.

Dundee is a nice place. Has changed a lot over the past few years. :)
 

Attachments

  • IMG_6311.JPG
    388 KB · Views: 20
  • IMG_6314.JPG
    371.1 KB · Views: 20
the grey connector with the orange levers are connecting everything together…. Someone beat me to it.


You want them separated.

Can I ask why you’re not putting mains powered and hardwire interlinked back up?
 
I hope that you're not intending to push those wires above the ceiling with just those connectors on, and not enclosed in a box intended for the purpose.
 

Reply to Smoke alarm replacement in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

I currently have a home with 7 interconnected, hard-wired smoke detectors. I have a hard-wired heat alarm in the garage that I need to have...
Replies
4
Views
1K
I've asked a similar question before I think and we came to the conclusion that apart from new houses and HMO's etc there aren't any rules about...
Replies
3
Views
310
I have a strip light in the kitchen operated from a single switch. I want to replace it with a straight bar 4 spot array. There are three supply...
Replies
2
Views
447
After 24 years my septic lift station pump and high water alarm needs to be replaced. It was tripping the breaker and the alarm was no longer...
Replies
5
Views
662
I'm about to order this wired smoke alarm system as it can network but I just went to see how my existing fire alarms are hooked up and there...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock