Currently reading:
Socket wired of a outdoor light!

Discuss Socket wired of a outdoor light! in the UK Electrical Forum area at ElectriciansForums.net

D

Dizzy_Maskell

Guys please back me up on this, went to a mates house and he has "proudly" shown me his DIY electrical handy work,

Few years back I ran a swa cable to the bottom of his garden tapped off the outside light as he wanted a light at the far end of the garden to for his shed etc.

He has adapted it now and added sockets to the shed for bits a pieces. But he has to turn the outside light on for them to be energised.

As he only uses the sockets whilst he is down there and so needs the light on anyway "there is no problem" can someone back me up so I can show him please as my qualifications don't appear to count.

Main switch 61008 on Con Unit and outside light circuit fed from down stairs lights 60898 B6.

Cheers
 
Starters for 10
1, Fused always blowing
2, Cable getting hot
3, Not enough volts at the end
4, You are working away in the shed and some divvy switches the lights off

You are right Trev nothing much to go wrong lol:shocked::32:
 
Serious guys, yes he has tapped into the JB with some 2.5 T&E to supply the sockets I've advised the issues but will not listen to me would some one write a official sounding post I can show him to get him to rip them out again
 
Serious guys, yes he has tapped into the JB with some 2.5 T&E to supply the sockets I've advised the issues but will not listen to me would some one write a official sounding post I can show him to get him to rip them out again

If he won't listen to a trusted friend then what makes you think he will listen to anyone else.

Phone your local building control tomorrow and ask there advice on what to do about someone who has carried out electrical work without complying with part P.
 
Has got kids? if so warn him of the possible, sorry probable, ramifications of this sort of botch job, because that's what it is, if that doesn't scare him, then he really is a muppet.
 
You could point out that where he's wired the sockets in 2.5mm, it then reduces to 1.5mm towards the CU, making his 2.5mm a bit pointless.
You could do a quick add up of the current likely to be used on the circuit - sockets, existing lights etc, see if it exceeds the rating of the breaker and point out if he uses that lot all the lights will go out, which is potentially dangerous. I think there's some reg about designing circuits to avoid this.
As already mentioned there's the volt drop to consider as well, which may no longer comply.

Put simply, the cable you put in was only designed for a light, not whatever he's running off the sockets as well.
 
If that was not a sarcastic comment then I'll suggest the regulation requiring RCD for any socket of less than 20Amps

If it was sarcastic then crack on!
Its got 61008 main switch RCD, it also has 6A MCB, worst can happen is he plugs in something rated higher and operates circuit devices. If he has done it, so what, it ain't OP's lookout.
 

Reply to Socket wired of a outdoor light! in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock