Badged01
And you're technical justification for that in-line with regulations would be .......You would not be doing it in my house or any of my jobs, straight out of the door tools first.......!!
Discuss socket in the UK Electrical Forum area at ElectriciansForums.net
And you're technical justification for that in-line with regulations would be .......You would not be doing it in my house or any of my jobs, straight out of the door tools first.......!!
I think its a good idea to show extremes when getting your point across XT but... you are just looking at overcurrent with the above example not fault current, also it would be completely unrecognised by electricians and therefore far more likely to cause problems and also its against the regs, whereas one 2.5mm spur from the origin would be ok for fault current, fairly recognised and adhere to the regs.
But!! If it was just a 2.5mm coming out of a 32A MCB with no ring then why not advise the housholder to change to a 20A MCB, you dont have to but it seems like a good idea.
Say it like it is Glenn
Well in this case it clearly doesn't comply. does it? if we don't comply then it's the slippery slope to butchery
I've always thought that the sole purpose of the Fuse/MCB was to protect the cable ie the MCB needs to be equal to or less than the maximum current carrying capacity of the cable. So in this case, the 32A MCB is not suitable.....
Yes, because it is total crap!! lol
So based on this assumption I could wire a single 13A socket on the end of some 1mm cable from a 50A MCB in the CU?
Overload protection does not have to be at the origin of the circuit...