Search the forum,

Discuss Solar PV Wiring Query - Compliance with BS 7671 in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

very unlikely that 2.5mm2 cable will comply

Thanks Gavin. Yes, SAJ manual says use 10 AWG / 6mm^ on AC side.

It’s an east-west array, 2x 8 panels. I think its power output will never be more than 2 kW, even in mid summer.

The house is a 3 storey terrace, tall and narrow. And the AC cable run is 8 meters, in plastic conduit (not steel like I said earlier), down the outside of the house, from eaves to CU.

I’ll mention all this to my landlady (again) and leave it in her hands. Thanks to everyone for the advice, especially the lads from Leeds.
 
Thanks Gavin. Yes, SAJ manual says use 10 AWG / 6mm^ on AC side.

It’s an east-west array, 2x 8 panels. I think its power output will never be more than 2 kW, even in mid summer.

The house is a 3 storey terrace, tall and narrow. And the AC cable run is 8 meters, in plastic conduit (not steel like I said earlier), down the outside of the house, from eaves to CU.

I’ll mention all this to my landlady (again) and leave it in her hands. Thanks to everyone for the advice, especially the lads from Leeds.

Why not get the installer back again and ask them to comply with the inverter's instructions manual which specifies a 6mm cable? They can bring a sheet of labels with them to do that bit correctly as well.

We would probably use an SWA down the outside wall rather than their method.

I think it will easily exceed 2kW at times. We have some e/w splits which clearly do more than that, hitting and exceeding 3kW at times. If the pitch is steep, 2.5kW might be a struggle.

But, then again, we wouldn't be using 2.5mm cable on the job to start with.
 
These guys have already had an opportunity to put it right and still haven't bothered.

Now think what the situation would be if no FiT and so people not "bothering" with MCS ...

Give 'em all a horse, they'll feel at home on it ...

If one of my apprentices installed a system to those standards, they wouldn't be employed the next day. Even they know far better than to do it like that.

I can see over a dozen non-compliance items in the second set of photos and description.
 
These guys have already had an opportunity to put it right and still haven't bothered.

Yes, I agree. I put everything I learnt from this forum in a nice simple list for them. Labels were No.3 on the list. They just can’t be bothered.

I think they’re doing 5+ installs per week. So I’ll email NAPIT and suggest NAPIT has look at some of their recent work.
 

Reply to Solar PV Wiring Query - Compliance with BS 7671 in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock