A silly fault in a circuit only 4m long is currently eluding me!

This is ECIR remedials of a landlords supply in a block of flats.
Circuit 2 = hall heater (just one). IR L+N > E of 1.23Mohms.

It's a very short circuit.
1 - Cable from CU up to Controller FCU. (about 50cm)
2 - Cable from Controller FCU to heater FCU, other side of wall. red dots show where. (about 3.5m)
3 - Cable from Controller FCU load to controller, right next to it. (about 20cm)
4 - filpilote control wire from controller to the heater. (about 4m)

The heater FCU is very creatively wired up as really it needs a 3 pole switch with fuse. But leaving that aside for now....

Heater completely disconnected > Same results.
All cables separated > every cable independently tests ok. Hmmmm.
N from the cable which runs from control FCU to heater FCU (i.e. the 2nd half of the radial) has 1.23Mohms IR to the CPC bar.

After a bit of head scratching the only thing I could thing of was one of the earthed metal clad boxes might have a fixing screw that had caught the cable, because the heater is directly behind where the CU is. But with all fixing screws removed for all of the boxes it's still showing this reading.

I ran out of time tonight, but I guess next step is to find out which CPC it has contact with to hopefully provide a clue.
Any other bright ideas? It's a plastic CU and plastic trunking.

1700244561182.png


This happens to be one of two identical buildings, and the the other one didn't have this fault.
 
Have you ruled out a fault within any of the accessories?
Thanks for the thought - I think so!
I just checked photo's...the core circled in red is faulting to the CPC bar.
The only CPC connected here is the load.
1700251108788.png

1700251130349.png

(the installer used the N half of the spur to connect the control cable and put the N in a choc block, it won't be going back like that)
Or a fault on a seemingly undamaged length of cable?
Every cable independently passes all IR tests.
There is some fault on the 2nd leg of cable causing a N to installation earth fault, but not a N-E fault on that cable.

Honestly, It would easy enough to run a new cable but I've become a bit obsessed with what is causing this when there is so little going on in such a small area!
 

Reply to Strange fault, any bright ideas? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all I don't appear to be able to post in the DIY forum so apologies if this is the wrong place. I live in a block of flats with an external...
Replies
3
Views
832
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Afternoon everyone.. During some testing I have found an IR reading of 0.01MΩ between N-E. This is on a length of SWA buried underground from the...
Replies
17
Views
3K
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
272

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock