Siracusa

DIY
Reaction score
0
I have a 20 amp gfci pool pump breaker that trips only when the pump is off during the night. Pool pump runs fine all day. I turn pump off manually at night by using the manual switch on a Intermatic pool timer. Watch it for 5 minutes and note that breaker remains in on position. Go out in morning and breaker is tripped. Breaker is in a protected box with no water intrusion, no rain on these days etc. The only item on the circuit is the 220 pump.

Pool timer pins have been removed temporarily so we dont worry about timer clicking on.

Since timer is after the breaker and is set to off, doesnt seem the timer or the pump itself should have anything to do with the tripping.

Any ideas? Many thanks
 
As it is a 240V pump, if the Intermatic timer contacts are only disconnecting one hot leg of the power feed, the motor windings can remain live via the other leg when switched off and therefore can still trip the GFCI if there is a problem. The ground leakage from the windings could be increasing as the motor cools down, either because a small amount of moisture is then able to build up, or just because something contracts as it cools.

The logical next step is an insulation resistance test of the motor windings both hot and cold.
 
As it is a 240V pump, if the Intermatic timer contacts are only disconnecting one hot leg of the power feed, the motor windings can remain live via the other leg when switched off and therefore can still trip the GFCI if there is a problem. The ground leakage from the windings could be increasing as the motor cools down, either because a small amount of moisture is then able to build up, or just because something contracts as it cools.

The logical next step is an insulation resistance test of the motor windings both hot and cold.
Super- very helpful.. thanks lucien
 

Reply to Strange pool pump breaker tripping in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

My customer wants to be able to switch his heat pump (3.5kW) for his swimming pool on and off remotely, he also wants to be able to set times for...
Replies
8
Views
649
I need advice regarding an electronic problem on my Hayward Power-flo Matrix pool pump. I notice that : 1. Neutral wire from source has become...
Replies
4
Views
2K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Hi, I hope that someone here might be able to put my mind at rest. I have an engineering mind and a reasonable understanding of electical work...
Replies
13
Views
2K
My pool pump (230V 1Ph cap start) US Motor k63cxdfw-5159 ) wasn't working so I started to look for a reason. I found the terminal to the output...
Replies
1
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock