OhmElectrical

Mate asked me can I look at his house after had it re wired by a bloke "on the cheap"

I noticed that the entire house was wired in 2.5mm.

Lights 60898 B6 - 2.5mm T&E
Sockets B20 - 2.5mm T&E
Cooker B32 - 2.5mm T&E (ring)
No shower

All RCD, bonding etc been done just wanted see if anyone ever seen this before
 
Mate asked me can I look at his house after had it re wired by a bloke "on the cheap"

I noticed that the entire house was wired in 2.5mm.

Lights 60898 B6 - 2.5mm T&E
Sockets B20 - 2.5mm T&E
Cooker B32 - 2.5mm T&E (ring)
No shower

All RCD, bonding etc been done just wanted see if anyone ever seen this before
lol guess he had a lot of 2.5mm

if everything else is order iinc testing i wouldnt be worried


what size is the bonding?
 
All seemed correct on that score tails upgraded the lot all bonded and even labelled up gas a water. I told him it's not wrong just not conventional although I suppose the guys does it rarely can just buy 1 drum a job done
 
Mate asked me can I look at his house after had it re wired by a bloke "on the cheap"

I noticed that the entire house was wired in 2.5mm.

Lights 60898 B6 - 2.5mm T&E
Sockets B20 - 2.5mm T&E
Cooker B32 - 2.5mm T&E (ring)
No shower

All RCD, bonding etc been done just wanted see if anyone ever seen this before

using 2.5mm on the lights must have been fun. Any 2 way switching?
 

Reply to Strange Techniques in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top