Been asked to install 3 X sockets 1 X light 1 X PIR light into a summer house. The building is 45 mtrs away from the house and I'm unable to wire back to the board. My plan is to take a fused spur of the ring and use a 4mm SWA to feed the summerhouse. In summerhouse I intend to install a 2 way garage unit for the circuits. My query is would you use a RCD main switch or a normal isolator. The ring Is RCD protected already. My other question is this a minor works or installation certificate. My thoughts are minor works as it is an alteration to an existing circuit.
Thanks.
 
Not everyone knows the answers to everything Davesparks we're not all blessed like yourself :tongue3:

Nothing wrong with asking others better methods, even if you do know the answers, confirmation is helpful, and sometimes we ask questions without thinking them through!

Hostility is now in the other forum, let it stay there.
 
I really don't have a problem with this sort of installation. I've just quoted to run a supply to a tiny summerhouse. They want a double socket to plug in a small tubular heater to take the chill off plus a radio and a couple of wall lights. No problem taking this off a socket circuit via a SFCU. Max load is probably going to be less than 3A.

On the other hand, I'm doing two 'garden office' supplies this week. Both on 32A dedicated circuits.
 
What you do in your own house is up to you, but if you sell that to a customer as an installation design then that's a different matter.

I don't see how spurring from a ring circuit to feed a summer house gives good segregation of circuits or minimises the potential disruption in the event of a fault.

I really don't see the point in replies like this, and the forum is risking going back to it's 'unfriendly' nature which it had a few months ago.

What is wrong with an FCU on the ring feeding a summer house with minimal load. Potential disruption is minimised, fusing is appropriate, RCD protection is in place. He's already looked in to going direct back to the board and can't so at least he's considered it.

Daz

Daz
 

Reply to Supply to summer house. in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top