Search the forum,

Discuss Swa Banjo? in the UK Electrical Forum area at ElectriciansForums.net

I use these when terminating into a plastic box. Great way to maintain earth continuity

20171107_094750.jpg
 
Hello everyone, having a debate with colleague, concerning SWA connected into metal CU. Can anyone advise the exact reason for the banjo, brass washer with cpc tag, is it compulsory rather than it just looks nice.
Any thoughts sound reasons would be nice also is it a requirement under the regs?
fainting.jpg
 
When using swa for the ‘tails’ I use 2 core 25mm swa and a 16mm earthing conductor in parallel

So what's the price comparison between the above and 3 core SWA?
I haven't got the charts on me at the mo but isn't the armour on 25mm sufficient for the earth?
 
The armour would not be 16mm equivalent copper as I’m talking about the main earthing conductor
Also if I used 3 core then a 25mm earth conductor is way overkill
 
The armour would not be 16mm equivalent copper as I’m talking about the main earthing conductor

That's what I was going on about. I will have to look that up as I thought it would be.
 
Just returning to the banjo's how many folk use brass bolts nuts & washers to secure the fly lead to the banjo?
I've lost count of the number of zinc plated roofing/trunking bolts I've seen on jobs with swa installed probably doesn't make a lot differance but it's looks right & is right.
 
Just returning to the banjo's how many folk use brass bolts nuts & washers to secure the fly lead to the banjo?
I've lost count of the number of zinc plated roofing/trunking bolts I've seen on jobs with swa installed probably doesn't make a lot differance but it's looks right & is right.
I always use M6 25mm brass nuts, washer and bolts as it’s always the way I was tought and is my preference.
Piranha nuts are a great alternative, tho when using larger glands say 32 mm and up,I’ve not seen them made for this size
 
The armour would not be 16mm equivalent copper as I’m talking about the main earthing conductor
Also if I used 3 core then a 25mm earth conductor is way overkill
The csa of the steele armour on a 25mm2 2core SWA equates to 60mm2 which in terms of CU eqates to 26.6mm2
 
I always use M6 25mm brass nuts, washer and bolts as it’s always the way I was tought and is my preference.
Piranha nuts are a great alternative, tho when using larger glands say 32 mm and up,I’ve not seen them made for this size
Piranha nuts 20mm to 32mm
 
What do you mean?
There are two comparisons for steel and copper.

One is where the conductor is to be used as a cpc and will have to withstand a very high current for a short period of time, in an earth fault.

The other is where the conductor is a bonding conductor and may in certain circumstances have to carry a significant current for a sustained period.

Steel is ~8.5 times worse at conducting electricity than copper but steel is better than copper at maintaining its integrity under thermal stress of high current.

So the where the steel is used solely as a cpc the combination of the two factors means steel comes out at about 2.25 times worse than copper for use as a cpc.

However where the conductor may have to carry long term current only the comparative resistances are considered and steel is then about 8.5 times worse than copper.

This means that for a cpc calculation the 60mm² steel armour in PVC /ST/PVC SWA is comparable to a 26mm² copper conductor in a cable.

For a bonding conductor calculation the 60mm² steel armour in PVC /ST/PVC SWA is equivalent to a 7mm² copper conductor in a cable.
 

Reply to Swa Banjo? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top