Discuss SWA Sub Main advice/comments in the Commercial Electrical Advice area at ElectriciansForums.net

Hi all, looking for a bit of advice and confirmation on my proposed plans for a SWA sub main to a ISO metal storage container. I've calculated the max demand in the ISO will be about 20A (300w of led lighting and 2 double sockets for chargers etc) It will be fed from a 3ph DB in another building. The cable run is 100 meters, I'm planning on using 16mm 2 core swa ( Volt drop calcs allow about 35A with 16mm) and installing a rod at the container (the vast majority of the cable run is at height, clipped to the building). The container will have a small 4 way board with RCD main switch.
The 16mm will be fed from a C32 breaker in the 3Ph board. Im installing double insulated 16mm tails and a 16mm earth from the 3ph DB to a meter (needs a meter installed) then from the meter to an adaptable box where I will terminate the SWA. Due to the fact that I'm using a rod at the other end, I'm planning on a 100ma S rcd for fault protection for the SWA (inside the adaptable box).
Can anybody see any glaring errors in my method? I have spoke to Napit and they were fine about my proposed plan, but they didn't mention the 100mA rcd.
Thanks in advance!
I take it the Earthing System for the upstream supply is a TN-C-S???
 
Haven't had a dig yet but I've been looking at bentonite if I'm struggling for a good reading.
Clay cat litter is cheaper and the same sort of stuff!

Obviously check for any buried services as far as you can. There are sites like this for main stream power & gas, but not everyone is on there:

Also remember that the main factor is soil conductivity is moisture, so if you can go deeper (say 8' = 2.4m rod, typically in two sections) you will generally do better than two short ones in parallel as more chance of the soil remaining moist.

I have used M16 stainless studding as an earth rod driven in like a giant drill (SDS adaptor and a 1/2" drive stud runner), but obviously you get purpose made ones and matching bit like access boxes, etc. For example:
 
Clay cat litter is cheaper and the same sort of stuff!

Obviously check for any buried services as far as you can. There are sites like this for main stream power & gas, but not everyone is on there:

Also remember that the main factor is soil conductivity is moisture, so if you can go deeper (say 8' = 2.4m rod, typically in two sections) you will generally do better than two short ones in parallel as more chance of the soil remaining moist.

I have used M16 stainless studding as an earth rod driven in like a giant drill (SDS adaptor and a 1/2" drive stud runner), but obviously you get purpose made ones and matching bit like access boxes, etc. For example:
Just did a job today where a house had no main earth. Did a Zs at the sockets and it was 290 Ohms. Did as bit of digging out, probably a couple of feet and got the 4ft rod pretty much all the way in. Ze of 28 ohms. That'll do for me!
 

Reply to SWA Sub Main advice/comments in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Replacing DB’s with all singing all dancing RCBO’s Problem’s we have now…Existing installation consisted of DB Grd Floor.. DB 1st Floor…Grd Floor...
Replies
11
Views
1K
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
742
Morning guys, I would like some advice, currently at my workplace, I am replacing a DB and existing wiring in a warehouse. One of the ways feeds...
Replies
4
Views
1K
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
890
Hi all, I would like some advice on a scenario currently at my workplace. I am replacing a Sub main DB and replacing the wiring to sockets/lights...
Replies
17
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock