Discuss Switched Fuse Spur in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
Wiring cooker hood into a switched fuse spur with a 13amp fuse in the spur. The cooker hood is 3amp. Should I swap out the 13amp fuse in the spur with a 3 amp fuse?
c70de5c5-e8c7-4ac6-af6c-82f557414300.jpeg
 
Instructions for the hood should tell you what fuse protection is required, but as a general rule a 3A would likely be the best choice.
 
The pics you put up of the consumer unit are all good .....all circuits RCBO protected and as above swap the fuse out for a 3 amp
 

Reply to Switched Fuse Spur in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I have a switched fuse spur where the cooker hood should plug in to… above the actual cooker. I was wondering if I could swap this out for a...
Replies
7
Views
583
Has anyone come across click accessories spurs burning out? it seems to only be happening with the CNS200 Trend uk Steibel eltron heaters Fuse...
Replies
7
Views
729
Should a small 500W electric rad on a fused spur also have an isolating switch? Some of these small rads have fancy timers that might get...
Replies
2
Views
434
DIY'er question: I have a singe switched fused spur above my kitchen counter, providing power to an undercounter fridge socket beneath it. The...
Replies
2
Views
421
I am using a 160watt-200watt multi uv tube stand alone sunbed,When the 2 power leads (plugs protected by 2x13amp fuses) plugged into a double wall...
Replies
9
Views
749

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock