Hi, what do you guys use to test rcbo trip times at the rcbo in DB? My Fluke test lead can not reach far enough for contact, I can't see any long reach probes for the Fluke 1662.
Any advice greatly appreciated :)
 
Make up some short (100mm) leads with a 4mm socket at one end and a bootlace ferrule at the other.
Put the bootlace end under the pinching screws and plug your test set into the other end. I always carry a couple of these leads and find them useful in many locations.
 
Make up some short (100mm) leads with a 4mm socket at one end and a bootlace ferrule at the other.
Put the bootlace end under the pinching screws and plug your test set into the other end. I always carry a couple of these leads and find them useful in many locations.
Thanks,sounds like a good work around. You'd think there would be long reach leads for this, looks like there is a gap in the market :)
 
I was going to suggest exactly the same; when test lead plugs split I keep them and use the plug other end to make up this sort of thing.

The other last resort solution, based on what I secretly used to do when I had a separate RCD tester that was only intended for socket circuits and had a moulded 3 pin plug on it and needed to test other circuits...

Stick an unswitched double socket in a surface pattress. Plug in the 3 pin plug lead for the fluke.
In the other half of the socket use a Megger/Kewtech etc 3-pin plug to 4mm lead, and any 4mm probes of your choosing. Rather a horrible clunky hack but works.
 
I was going to suggest exactly the same; when test lead plugs split I keep them and use the plug other end to make up this sort of thing.

The other last resort solution, based on what I secretly used to do when I had a separate RCD tester that was only intended for socket circuits and had a moulded 3 pin plug on it and needed to test other circuits...

Stick an unswitched double socket in a surface pattress. Plug in the 3 pin plug lead for the fluke.
In the other half of the socket use a Megger/Kewtech etc 3-pin plug to 4mm lead, and any 4mm probes of your choosing. Rather a horrible clunky hack but works.
Thanks, I might get myself on dragons den with some long probes, see if any of them wanna back it :)
 
Long reach probes are a bad idea for sparks as you might be tempted to use them in inappropriate locations. Tim's idea works and is safe but as he says a bit clunky. The little 4mm to bootlace leads are easy to stick in a corner of your tool bag so they are always handy.
 
Long reach probes are a bad idea for sparks as you might be tempted to use them in inappropriate locations. Tim's idea works and is safe but as he says a bit clunky. The little 4mm to bootlace leads are easy to stick in a corner of your tool bag so they are always handy.
thanks for your help :)
 

Reply to TEST LEADS FOR RCBO TESTING in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Just wondering if someone could help provide an explanation as to why this might be the case when testing an RCBO. Testing the RCBO at the DB...
Replies
7
Views
325
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
Ring main was on a c40 rcbo so I tested the circuit everything was fine and dropped down onto a b32, It’s quite a long circuit but only serves...
Replies
26
Views
2K
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
530
Hi, Just been scratching my head about this one and wonder if I've missed anything. A few weeks ago I installed a new circuit for a 3kw oven and...
Replies
6
Views
877

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock