Hi all,
I have recently finished a job and need to do the necessary tests to fill out the MWC. Can I do the earth fault loop impedance test with all lights on as this is in an office environment and switching all lights off is not practical. Also doing the insulation resistance test is not possible as it's not possible to disconnect all the lights in the circuit. Would this go down as a limitation. Might see if the client will allow me to go in and do it on a Sunday so I can isolate the circuit and not disrupt anything. Thoughts please.
Thanks
 
What work have you actually carried out, is it an alteration or a new circuit, if it's the later (a new circuit) the a MNW certificate isn't applicable you would need an EIC to record your test results.

Your client is not being very helpful he or she requires a certificate for insurance purposes, by not allowing you access is, to be honest plain stupidity. those are my thoughts anyway.
 
In this sort of situation I would IR test the new work I had done, not necessarily the whole of the existing circuit.

Yes you can do a Zs test with loads connected, but some loads might cause so much electrical noise that the meter may fail to complete the test. Fluorescent lights may be an example of such a load.
 
What work have you actually carried out, is it an alteration or a new circuit, if it's the later (a new circuit) the a MNW certificate isn't applicable you would need an EIC to record your test results.

Your client is not being very helpful he or she requires a certificate for insurance purposes, by not allowing you access is, to be honest plain stupidity. those are my thoughts anyway.
It is an addition to the lighting circuit where I have added an extractor fan to dissipate heat from the server room so MWC it is.
 
In this sort of situation I would IR test the new work I had done, not necessarily the whole of the existing circuit.

Yes you can do a Zs test with loads connected, but some loads might cause so much electrical noise that the meter may fail to complete the test. Fluorescent lights may be an example of such a load.
So I would need to IR test from where I connected to the existing to the SFCU that I installed and then from SFCU to appliance. It is all fluorescent lights in the suspended ceiling tile type and lots of them.
Thanks for the replies.
 
So I would need to IR test from where I connected to the existing to the SFCU that I installed and then from SFCU to appliance.

Er, yes. But why not just leave the SFCU switched on and IR test the whole of the new wiring in one go?

Anyway, how did you connect to the existing wiring if you couldn't isolate the circuit (and turn off the lights)?

And surely you did an IR test before connecting and energising the new wiring?
 
Last edited:
Er, yes. But why not just leave the SFCU switched on and IR test the whole of the new wiring in one go?

Anyway, how did you connect to the existing wiring if you couldn't isolate the circuit (and turn off the lights)?

And surely you did an IR test before connecting and energising the new wiring?
I did isolate the light circuit which was looped in the switch so easy one to connect to buy no didn't do IR test before switching it back on as all the lamps are still connected. Or do you mean just the new bit? If so then no I didn't!!! Will remember that in future. Lots of people had to work in the dark for a little bit.
 
I find that a bit strange, before connecting to the existing circuit,surely you would conduct your dead testing before energising the new additional circuitry anyway.?
 

Reply to Testing for MWC in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
899
Had an enquiry where the installation (commercial) is relatively new and client has requested a condition report. Probably 80-100 circuits plus...
Replies
8
Views
1K
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
664
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
704
Hello everyone, Hope you're all well. I'm carrying out an overall/global insulation resistance test on a newly wired 3 phase installation we did...
Replies
24
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top