Hi I'm about to start my testing course and started looking though my GN3 and I've got a question one of you lads could answer for me.
when doing insulation resistance test it states that all neon, dimmers, lamps and other sensitive equipment should be removed.
My question is do you remove all electrical items from the circuit, either by isolating or unplugging.
If so what would you do if you couldn't remove one, say there was a tv mounted to the wall and you couldnt get to the socket behind.
thanks in advance
 
in that case you would not IR test L-N unless youy have funds to purchase a 42" LCD TV after you've fried it.
 
Discussion time or Tin Hat...... OSG Page 10 612.3.2 . Where SPD's or other equipment (lah lah lah) or may suffer damage. Not practical to disconnect, test at 250V dc and at least 1Mohm. I personally start at 250 to see what's there. (Just in case).
 
Code it up as you cannot get access to a point of isolation and dont IR it.
In practice you are going to have to get used to stuff spoiling a good IR test.
Great for newly installed ccts but troublesome on well established lighting and socket ccts. I always use 250V setting for stuff i have not installed and on final ccts that are not simply point to point, this will do for 99% of the time but please dont mention it in an exam... lol

actually just had a look at the OSG to see if it allows reduced voltage testing and it is a recommendation as mentined above. There is also the option to tie LN together but TBH i really dont like the idea of LN tied and 500V, maybe my in-experience showing but i like 250V setting and i haven't blown anything up yet.
 
Last edited:
When you think you've unplugged everything and your still getting a low reading and then find the Ariel booster tucked away in the loft somewhere. Happy days!
 

Reply to Testing question in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock