What is the fastest RCBO you know?
Fastest is meaning it has the lowest trip times.
Right..... so making an assumption that we're talking about a 5x figure (as most faults are in fact likely to be close to ADS levels) then typically in my experience of testing AC types I'm seeing numbers around 8ms - 12ms area for most manufacturers. HOWEVER - in type A RCD devices we are now typically seeing longer disconnect times at 1x than we used to (and we no longer have to test at 5x). So, if you have two RCD's in series it is still a game of chance as to which may trip first and as others have said is also entirely dependant on a heap of other factors and physics at play.

If you're experiencing nuisance tripping, as I suspect is the case, then you need to look at the cause of the fault, not the characteristics of the protecting devices.
 
There is no such thing as instantaneous cause and effect in the way you are imagining it. Even if the device operated at the speed of light, (around 300,000 Km per second = 186,282 miles per second) it would still take an extremely small amount of time to operate . Albeit, this would be so fast, possibly immeasurable, so for all intent purposes as close to your instantaneous as you could get.

Even at this high speed the sun's light doesn't reach Earth until around 8.3 minutes after it was initially propagated, and the nearest star to ours, just over 4 years!

But things start to get even more mind boggling when you delve into Albert Einstein's relativity which describes the relationship between space, time, speed and measurements.
Extremely small amount of time is the key to my problem.
Logically, to measure any current, leakage current or normal current, we need a time, small amount of time. Now is to manufacturers to build different devices with different sensibility for different applications. I would like to identify the most sensitive RCB.
The electrical wires length in the house comparing to distance to the Sun is nothing, so I assume the speed of current is instantaneous, in my house. The distance between two RCB is too small to have any delay so the waveform is synchronous, I think.
 
Right..... so making an assumption that we're talking about a 5x figure (as most faults are in fact likely to be close to ADS levels) then typically in my experience of testing AC types I'm seeing numbers around 8ms - 12ms area for most manufacturers. HOWEVER - in type A RCD devices we are now typically seeing longer disconnect times at 1x than we used to (and we no longer have to test at 5x). So, if you have two RCD's in series it is still a game of chance as to which may trip first and as others have said is also entirely dependant on a heap of other factors and physics at play.

If you're experiencing nuisance tripping, as I suspect is the case, then you need to look at the cause of the fault, not the characteristics of the protecting devices.
Yes, you are right. I have two RCD in cascade, first in the main distribution board and second is integrated in the portable power strip.
I had the same thoughts about nuisance tripping. When I touch the phase wire to the earth, this may cause different peaks so this nuisance could trigger both RCD (not confirmed by measure). What about integrate an anti nuisance filter in the power strip?
 
Out of interest, why do you keep experiencing this regular tripping of your RCDs?
 
Out of interest, why do you keep experiencing this regular tripping of your RCDs?
I'm searching to have a security device, in this case a power strip with integrated RCD to trigger while the upstream RDC remains ON. Is a question of sensitivity and rapidity. When you buy a fast and sensible RCD that is intended to trigger faster (to protect sensitive devices for example) than other but in real life is useless because I still need to open the main distribution board to reactivate the main RCD. With this portable 10mA RCD or without - is the same thing, the main RCD is triggering. There should be a way to protect small circuits without cutting off all the house.
 
I'm searching to have a security device, in this case a power strip with integrated RCD to trigger while the upstream RDC remains ON. Is a question of sensitivity and rapidity. When you buy a fast and sensible RCD that is intended to trigger faster (to protect sensitive devices for example) than other but in real life is useless because I still need to open the main distribution board to reactivate the main RCD. With this portable 10mA RCD or without - is the same thing, the main RCD is triggering. There should be a way to protect upstream small circuits without cutting off all the house.

But if you are getting repeated tripping of an RCD then you have something wrong somewhere. Are you getting tripping of your RCD?
 
A 10mA RCD trips between 5mA and 10mA. A 30mA RCD trips between 15mA and 30mA. Any differential fault current that exceeds the tripping current of that particular 30mA RCD is equally likely to trip either or both RCDs.
You will only get discrimination if the fault current exceeds the tripping current of the 10mA RCD but is less than that of the 30mA one.
You can, of course, replace the 30mA RCD with a 'S' type delayed version, but then the rest of the circuits supplied by that RCD will not have the required level of protection.
 
But if you are getting repeated tripping of an RCD then you have something wrong somewhere. Are you getting tripping of your RCD?
No, I don't have repeated tripping. I simulate a fault. Both RCD shuts off when I want only one to shut off, the closest to me and to the fault
 

Reply to The fastest RCBO in the world in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Just wondering if someone could help provide an explanation as to why this might be the case when testing an RCBO. Testing the RCBO at the DB...
Replies
7
Views
325
Hi just wondering if someone can help me. I have an rcbo that keeps tripping but only when the fly earth and neutral lead on the bars it trips...
Replies
10
Views
550
2 questions.. 1. Will the mini Starbreaker RCBO's fit in this board? Below is a picture of the board and also the type of RCBO I want to fit in...
Replies
3
Views
371
I’m probably going to look stupid here, but it will be worth it if I get the answer 😆, as I can’t fathom it out. I’ve never really thought of it...
Replies
22
Views
879
Folks. I need to install a defib unit outside on a wall. Does this require an RCBO or not, just wondering as the unit has a small heater within...
Replies
15
Views
575

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock