Discuss Three phase motor ( Power cable faulty phase ) in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hi gentlemen,

I have three phase motor has an issue. This motor is star connection. When I just disconnect the power cable coming from MCC through breaker, and did megger test I found the reading as follows:

Phase1 with ground = 0.17 MOhm
Phase 2 with ground = 250 Mohm
Phase 3 with ground = 4.5 Mohm

Between phases each one with other = 550 Mohm

And I checked the motor winding they are in good condition

The question here due to power cable reading it shows me that conductor 1 ( phase 1 ) is faulty and the whole cable need to be replaced right !!!!?

Now, the big question is

While I have this bad reading for the cable why when I energized the motor the breaker not tripping ( the motor still working healthy without any trip ) !!!!!!!

Please note that in my breaker in MCC room I don’t have ground fault relay and no CT only breaker fuse for protection and overload contacts

Is this the cause why the breaker not tripping due to there is no ground fault relay !!!?

Thanks all
 
Phase 1 with ground = 0.17 MOhm
Phase 2 with ground = 250 Mohm
Phase 3 with ground = 4.5 Mohm

Between phases each one with other = 550 Mohm
Are you sure that is only the cable you are testing, and no other control gear, etc, present?

I am just wondering how P1-G and P3-G is not reading around 4.7M if you measure P1-P3 unless there is some voltage-dependant device present somewhere (e.g. some surge protection in some electronic control system, etc). Though it could be failing insulation at (presumably) 500V test voltage which is not apparent and lower voltages.

Are the end points of the cable clean and free of any conductive dust or moisture? (If DC motors in use then graphite dust from the brushes wearing can drop IR reading but can be cleaned up with a bit of care and solvent to being things back to good).

And I checked the motor winding they are in good condition

The question here due to power cable reading it shows me that conductor 1 ( phase 1 ) is faulty and the whole cable need to be replaced right !!!!?
If it is an internal cable fault then you probably should replace the whole cable as quite possibly the others are going as well. E.g. P3 is heading down towards P1 reading it seems..

While I have this bad reading for the cable why when I energized the motor the breaker not tripping ( the motor still working healthy without any trip ) !!!!!!!

Please note that in my breaker in MCC room I don’t have ground fault relay and no CT only breaker fuse for protection and overload contacts

Is this the cause why the breaker not tripping due to there is no ground fault relay !!!?

You don't give other details of motor size, operating voltage, or even which country you are in to know what conventions are in use.

Here in UK (and similar in EU) most LV supplies are 400V/230V 3-phase so 0.17M to ground is only going to have 1.4mA or so flowing and that is not going to trip any common RCD/GFCI, certainly not the higher threshold delay-type seen for bigger power system protection.

But it is worryingly low and could indicate a fault will be coming your way at some point soon, and depending on the size of your system and the consequences of short circuit or an unplanned shutdown that could be very expensive or possibly dangerous.
 
Last edited:
As per @pc1966 the faults from L1 and L3 to ground should appear in series as a fault L1-L3. The measured resistance L1-L3 might not be exactly the sum of the two, but one would expect it to be lower than the measurements for L1-L2 and L2-L3. It might be worth double-checking those readings before choosing what to do next.
 

Reply to Three phase motor ( Power cable faulty phase ) in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a scenario where there is a three phase DB in a commercial property where there are mixture of three phase and single phase washing...
Replies
2
Views
840
Hi there, I built a house with ground source heating 5 years ago and it's a fairly large house so I have 3 phase supply 80 amps per phase. I had...
Replies
7
Views
937
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
579
Hi, this might be an easy question, but i need to power a single phase motor situated about 300 meters away from my MCC. Do I just run 3 phases...
Replies
6
Views
1K
Hello, my name is Kelvin. I'm a trainee hydraulic engineer in Indonesia. I apologize if this question has been answered before / if this question...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock